Results 1 to 7 of 7
  1. #1
    Join Date
    Jul 2007
    Posts
    65

    u/h's sharing same venting

    Came across a Lennox U/H with ventor motor sharing common vent with ICP U/H with natural draft. Besides code, why is this a wrong situation?

  2. #2
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    508
    Venting into a chimney, B Vent stack or like a side wall? If its a properly lined chimney or B Vent stack and its sized properly why couldn't they share?

  3. #3
    Join Date
    Jun 2004
    Location
    St Paul, minnesota
    Posts
    766
    natural draft water heaters with a draft induced furnace is installed on millions of residential homes without any problems, provided closest one to the main stack is "saddled in"

  4. #4
    Join Date
    Nov 2011
    Location
    British Columbia
    Posts
    48
    No code issue in BC, as long as the vent and both connectors are correctly sized.

  5. #5
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,871
    Ideally the power vented unit should be tied into the chimney by itself, above the natural draft unit.
    Recently I responded to a CO spill coming from a water heater sharing a common vent pipe with a power vented boiler, when both appliances ran at the same time the positive pressure created by the boiler limited the water heaters combustion air and venting resulting in poor combustion,soot and CO spilling.

  6. #6
    Join Date
    Nov 2011
    Location
    British Columbia
    Posts
    48
    Have to clairify myself. No problem so long as both units are a Cat I appliance - nameplate would say so. Cannot connect atmospheric unit into postive pressure vent for obvious reasons.

  7. #7
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    3,008
    Quote Originally Posted by RuralSpaceman View Post
    Have to clairify myself. No problem so long as both units are a Cat I appliance - nameplate would say so. Cannot connect atmospheric unit into postive pressure vent for obvious reasons.
    That hasn't stopped people from trying. Saw a positive pressure furnace and wh on same pvc flue one time. hx in furnace got the smackdown from wh backflow
    Col 3:23