    Duct Problems

    Today i had a water source heat pump feeding a classroom and 3 offices. It has a main trunk line with 8" taps coming off of it. There are a total of 7 taps on this unit. 4 for the classroom and 1 for each office. Well the problem i am having is the one diffuser nearest to the unit isn't putting out hardly any air. I pulled the duct off and inspected inside the duct. At this point in the duct, it is like there is a dead spot. The air is just turbulating around the opening. This duct tap comes off right after the flex connector. It is the first fed. The diffusers that come off further down the main get plenty of air. Why is this? What can i do to the ducting to fix this problem? The office with the problem has the stat. So it is causing no heat or cool to go into the room. So it either burns everyone out or freezes everyone out depending.

    Thanks for the help!
    J. King

  2. #2
    Join Date
    Sep 2007
    Location
    Boise, ID
    Posts
    5,013
    Post Likes
    Too high of velocity, the air just blows on by. Add a scoop.

    Oops, hope that aint DIY. If so a mod can remove and spank me.
    Politicians need to be changed like diapers, and for the same reason.
    Mark Twain

  3. #3
    Join Date
    Oct 2007
    Location
    Milwaukee,WI
    Posts
    1,114
    Post Likes
    How many people have messed with the downtream dampers to get more/less heat or cooling in their office?

    A simple professional re-balance may help things. Either that or it may not have been properly balanced in the first place.
    ___________________________

    Chicago is an indian word for stinky!!!!!!
    -supertek65

  4. #4
    Join Date
    Oct 2010
    Location
    AZ
    Posts
    647
    Post Likes
    How far away is this duct from any changes in direction?
    Is there a long section of straight duct before the tap or is it right after a change in direction?
    Do you have shoe taps?

  5. #5
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    Too high of velocity, the air just blows on by. Add a scoop.

    Oops, hope that aint DIY. If so a mod can remove and spank me.


    Yea i was thinking that, but i just didn't know how much that would help. I haven't used them that much. I heard something from a sheet metal guy stating that the air is more even at the end of the trunk.

    How many people have messed with the downtream dampers to get more/less heat or cooling in their office?

    A simple professional re-balance may help things. Either that or it may not have been properly balanced in the first place.


    Actually every damper is open all the way down the trunk line.

    How far away is this duct from any changes in direction?
    Is there a long section of straight duct before the tap or is it right after a change in direction?
    Do you have shoe taps?


    The main duct just comes straight off of the heat pump, goes into a flex connector, and is just a straight run all the way to the end cap. The duct doesn't change directions or switch sizes. The tap with the problem is right up next to the discharge of the unit. There is no long straight run before the taps.

    Shoe taps? Are they taps with scoops?
    J. King

  6. #6
    Join Date
    Sep 2007
    Location
    Boise, ID
    Posts
    5,013
    Post Likes
    Might want to relocate the takeoff further down the duct where there is less turbulence and and the velocity has slowed, probably the easiest solution.
    Politicians need to be changed like diapers, and for the same reason.
    Mark Twain

  7. #7
    Join Date
    Oct 2011
    Location
    Arkansas
    Posts
    844
    Post Likes
    Quote Originally Posted by apprentice3 View Post
    Today i had a water source heat pump feeding a classroom and 3 offices. It has a main trunk line with 8" taps coming off of it. There are a total of 7 taps on this unit. 4 for the classroom and 1 for each office. Well the problem i am having is the one diffuser nearest to the unit isn't putting out hardly any air. I pulled the duct off and inspected inside the duct. At this point in the duct, it is like there is a dead spot. The air is just turbulating around the opening. This duct tap comes off right after the flex connector. It is the first fed. The diffusers that come off further down the main get plenty of air. Why is this? What can i do to the ducting to fix this problem? The office with the problem has the stat. So it is causing no heat or cool to go into the room. So it either burns everyone out or freezes everyone out depending.

    Thanks for the help!
    How long is the plenum?

    Usually with that many take offs and a long plenum, it's best to reduce it. A scoop would help, but a new properly sized plenum would be the best solution.

  8. #8
    Join Date
    Sep 2011
    Location
    Vancouver, WA
    Posts
    264
    Post Likes
    Quote Originally Posted by apprentice3 View Post
    Too high of velocity, the air just blows on by. Add a scoop.

    Oops, hope that aint DIY. If so a mod can remove and spank me.


    Yea i was thinking that, but i just didn't know how much that would help. I haven't used them that much. I heard something from a sheet metal guy stating that the air is more even at the end of the trunk.

    How many people have messed with the downtream dampers to get more/less heat or cooling in their office?

    A simple professional re-balance may help things. Either that or it may not have been properly balanced in the first place.


    Actually every damper is open all the way down the trunk line.

    How far away is this duct from any changes in direction?
    Is there a long section of straight duct before the tap or is it right after a change in direction?
    Do you have shoe taps?


    The main duct just comes straight off of the heat pump, goes into a flex connector, and is just a straight run all the way to the end cap. The duct doesn't change directions or switch sizes. The tap with the problem is right up next to the discharge of the unit. There is no long straight run before the taps.

    Shoe taps? Are they taps with scoops?
    The rule of thumb I use is the first tap has to 3 times the diameter of the duct away from the discharge of the unit. So if the duct is 8" dia, then your first tap is set at 24" away from the unit. This also applies to change of directions.

  9. #9
    Join Date
    Jan 2001
    Location
    Pamnyra VA.
    Posts
    710
    Post Likes
    Is there a transition in duct size anywhere along the main trunk?There should be after a few taps are taken off.This will add pressure to your outllet.

  10. #10
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    Gibby, I like this suggestion

    Quote Originally Posted by Gib's Son View Post
    Might want to relocate the takeoff further down the duct where there is less turbulence and and the velocity has slowed, probably the easiest solution.
    I'd be a little uncomfortable with a "scope" that might really disrupt the high velocity air stream coming off the unit as per your first thought
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  11. #11
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    +1

  12. #12
    Join Date
    Sep 2007
    Location
    Boise, ID
    Posts
    5,013
    Post Likes
    Quote Originally Posted by genduct View Post
    I'd be a little uncomfortable with a "scope" that might really disrupt the high velocity air stream coming off the unit as per your first thought
    I kinda missed the turbulence word first time around. That being said, I have seen it many times with high velocities that the air just rushes on by the first branch.
    Politicians need to be changed like diapers, and for the same reason.
    Mark Twain

  13. #13
    Join Date
    Jul 2011
    Location
    Columbus, Ohio
    Posts
    136
    Post Likes

    No static man

    Sounds like you have no static pressure. Too many openings or too many air exits to allow for static pressure to build up and push the air out of the closest registors. Close down some of the dampers until you get static pressure in the trunk. I Should think you would need a 1/2 inch or so of pressure at 2/3 down the trunk run, on a unit that size.

  14. #14
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    An interesting thought

    Quote Originally Posted by synergy View Post
    Sounds like you have no static pressure. Too many openings or too many air exits to allow for static pressure to build up and push the air out of the closest registors. Close down some of the dampers until you get static pressure in the trunk. I Should think you would need a 1/2 inch or so of pressure at 2/3 down the trunk run, on a unit that size.
    But don't you agree that close to the unit discharge we have all velocity pressure and won't have any static til the airstream slows down and we see the static regain we are looking for?
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  15. #15
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    Hey Gibby, just remembered

    Quote Originally Posted by Gib's Son View Post
    I kinda missed the turbulence word first time around. That being said, I have seen it many times with high velocities that the air just rushes on by the first branch.
    A number of years ago we installed a make-up air unit for an industrial printing press. The mechanical insisted on a high velocity supply since the run was short and the we had plenty of fan on this extended plenum kind of design. well the air was moving around 1800 FPM and actually sucked air in on the first supply register. Just thought of that looking at your post. Funny huh?
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  16. #16
    Join Date
    Jul 2011
    Location
    Columbus, Ohio
    Posts
    136
    Post Likes

    Static

    Static pressure should be at its higest at the fan exist and at its lowest at the end of the run, this is due to friction loss through the duct. The duct internal area and the number of exits need sized and balanced so as the air supplied to the duct is slightly higher than the air leaving the duct. This creates static pressure. Static pressure forces the air out of the registors. With out static pressure, the air will travel down the duct and the velocity pressure will force the air out at the end runs only. You need to have a pressurised duct to get even air flow to all supplies. How much static varies from type of system.

  17. #17
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by genduct View Post
    But don't you agree that close to the unit discharge we have all velocity pressure and won't have any static til the airstream slows down and we see the static regain we are looking for?
    Velocity pressure only exists with static pressure.

    You can have static without velocity though.

  18. #18
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    Hey Second

    Quote Originally Posted by second opinion View Post
    Velocity pressure only exists with static pressure.

    You can have static without velocity though.
    I agree with your quote but without motion what would be the point of a system that wasn't delivering anything?

    Me and Mr Bernoulli Think of TOTAL Pressure the same way you think of WATTS You know Volts time Amps. Key being the watts stay the same and as the velocity slows the static builds. Now that doesn't mean there is all velocity pressure at the discharge just mostly velocity pressure.

    That's my understanding of the Physics of the situation. If you see any flaws or have a simpler explanation, you know me, I am always open to being educated
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  19. #19
    Join Date
    Nov 2011
    Posts
    4
    Post Likes
    Is this a new unit? Has the unit and duct been sized correctly? Has it been balanced?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •