Hello everyone,
I have a design where there is a walk in food cooler, walk in freezer and a walk in beer cooler.
The CHWS/CHWR temps currently is at 44'F/55'F. We need to increase the supply to 60'F.
Do I need a pump to do this. Also what other equipment do I need to increase this temperature.
Can you also please direct me to schematic showing this arrangement.
Thanks in advance for the help.
-
11-16-2011, 04:38 PM #2
What are your water pressures?
-
11-16-2011, 05:55 PM #3
Why do you need to increase the supply temperature to 60ºF?
If your refrigeration condensing units are standard water-cooled models, they will be equipped with condenser water regulating valves which will throttle the flow to maintain proper condensing pressures.
Am I missing something?
-
11-16-2011, 08:24 PM #4
-
11-17-2011, 08:57 AM #5
Regular Guest
- Join Date
- Jun 2010
- Location
- Miami
- Posts
- 249
It would be the difference between supply and return chill water pressure that the Penn valve is concerned with. For energy consumption resons one wouldn't want that to be a very large difference. It should be well under what city water pressure dumped to drain would be and any Penn valve will handle that with ease.
If it is really necessary to raise the loop temp to 60 degrees a 3-way mixing valve could be used. I see no need for one though. Frankly I run condensers off cooling tower water. The water treatment chemicals are more in line with what you need for the condenser to prevent scale.
-
11-17-2011, 09:23 AM #6
Regular Guest
- Join Date
- Sep 2011
- Location
- Vancouver, WA
- Posts
- 180
-
11-29-2011, 08:27 PM #7
Professional Member
- Join Date
- Sep 2011
- Location
- Augusta, ME
- Posts
- 69
yeah i have seen pressure reducing valves used for that very reason. then allow the penn valve to regulate head pressure and sc.