Why do almost all refrigeration sys. use pump down?
I have a idea of what pump down is for, but why does it seem like on most walk ins, and split system refrigeration systems use pump down? Does it assist in defrosting the coil during the off cycle. I am told that it prevents liquid migration, and allows ease of start up of the compressor. What else does it do?
Thank YouJ. King
-
11-14-2011, 09:39 PM #2
Professional Member*
- Join Date
- Jun 2007
- Location
- Williamsport, PA
- Posts
- 144
It also makes installation easyer by not having to wire a thermostat back to the condensing unit.
-
11-14-2011, 09:54 PM #3
Professional Member
- Join Date
- Apr 2001
- Location
- Camel City, NC
- Posts
- 6,221
agreed and
If the solenoid is wired off the fan circuit and the help turns the fans off to stock the cooler because it's to cold in there, you don't slug the compressor. The system just pumps down.
Walk-in freezers should be pump down in off cycle and defrost to prevent flood back on start-up.Be safe not fast. body parts don't grow back
-
11-14-2011, 11:50 PM #4
Professional Member*
- Join Date
- Oct 2003
- Location
- las vegas
- Posts
- 1,505
-
11-15-2011, 12:07 AM #5
To help prevent liquid migration to the compressor,more so with units with head masters that use extra gas. Outdoor units cannot cycle on pressure where the temp gets colder than the cut in.
-
11-15-2011, 04:50 PM #6
Regular Guest
- Join Date
- Jan 2005
- Location
- texas
- Posts
- 110
In a nut shell, whenever the volume of liquid refrigerant in the system, and the internal volume of the evaporator and suction line assembly exceeds the amount the compressor can safely handle(vaporize and compress),a pump down is needed.
-
11-15-2011, 05:09 PM #7
It also allows you to run more than 1 indoor circuit off the same condensing unit.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
11-18-2011, 02:51 AM #8
Regular Guest
- Join Date
- Nov 2011
- Posts
- 21
we should phase out the pump down and utilize inverter and PLC technology
can anyone go into more detail about the new systems out there now how they vary the frequency of the compressor etc instead of shutting it completely off?
would this be correct?
just starting out
-
11-18-2011, 09:31 PM #9
Professional Member
- Join Date
- Oct 2011
- Location
- Hull
- Posts
- 53
With a drive who drop in frequency but im not sure its possible with a single compressor unit
-
11-18-2011, 11:44 PM #10
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,642
-
11-19-2011, 07:51 AM #11
Regular Guest
- Join Date
- Nov 2011
- Posts
- 21
-
11-23-2011, 07:36 PM #12
Regular Guest
- Join Date
- Sep 2011
- Location
- Plainfield IL
- Posts
- 101
Guys from Texas will claim you dont need a pump down cycle but you do so you dont want to flood out your compressor with liquid freon during the off cycle.
Also a defrost clock, in my book is a must, for ALL walk in cooler applications. That is if you dont want problems!
Evan
-