Thread: YCAS H.P.C.O.
-
11-13-2011, 08:38 PM #1
Professional Member
- Join Date
- Mar 2010
- Location
- Southeast Michigan
- Posts
- 36
YCAS H.P.C.O.
I'm working on a york chiller YCAS0250EC46XFADB I need to replace the mechanical high pressure cutout. My question is if there is a schrader valve were the H.P.C.O connects to the side of the compressor? Or do I have to isolate the compressor and recover before replacing? Thanks
-
11-13-2011, 11:47 PM #2
Professional Member
- Join Date
- Sep 2011
- Location
- Northwest Louisiana
- Posts
- 158
You will have to isolate and pump out compressor or install manual reset HP switch to another high pressure port until you can.
A LITTLE BIT OF STUPID GOES A LONG WAY!
-
11-14-2011, 10:07 AM #3
Professional Member
- Join Date
- Mar 2010
- Location
- Southeast Michigan
- Posts
- 36
Thanks for the info


Reply With Quote