    YCAS H.P.C.O.

    I'm working on a york chiller YCAS0250EC46XFADB I need to replace the mechanical high pressure cutout. My question is if there is a schrader valve were the H.P.C.O connects to the side of the compressor? Or do I have to isolate the compressor and recover before replacing? Thanks

  2. #2
    Join Date
    Sep 2011
    Location
    Northwest Louisiana
    Posts
    290
    You will have to isolate and pump out compressor or install manual reset HP switch to another high pressure port until you can.
    A LITTLE BIT OF STUPID GOES A LONG WAY!

  3. #3
    Join Date
    Mar 2010
    Location
    Southeast Michigan
    Posts
    40
    Thanks for the info