if your talking about the orange electronic switch, it sends 24 back.
-
06-06-2012, 08:35 PM #16
-
06-06-2012, 08:36 PM #17
-
06-09-2012, 11:19 AM #18
Regular Guest
- Join Date
- Sep 2011
- Posts
- 12
I Think I know how to bypass the internal carrier chiller flow sensor. The flow sensor has a ground, a 24vac input, and a 0-24vdc output. A person might want to bypass it if they want to install a cheaper inline flow switch.
This is for the three wire flow sensors.
Get a small plug-in transformer that outputs 24vdc and plug it in to the 120v power outlet in the chiller. Connect the 24vdc negative to the ground and connect the 24vdc positive to the main board where the 0-24vdc output wire of the sensor connects. This will tell the board there is water flowing through the lines.
-
06-09-2012, 11:54 AM #19
Yea, you have done this before?
no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
06-09-2012, 12:05 PM #20
On comfort link system all you need to do is at the mbb j7 there is two orange wires that go to flow switch contacts. Take them to new mechanical flow switch or jumper to test.
-
06-09-2012, 04:15 PM #21
Regular Guest
- Join Date
- Sep 2011
- Posts
- 12
-
06-09-2012, 04:19 PM #22
Regular Guest
- Join Date
- Sep 2011
- Posts
- 12
I was called out to a carrier chiller that wasn't working and found the plug that plugs into the flow sensor was corroded beyond repair and carrier did not have one in stock locally so we had to order overnight. I was looking for a way to bypass the flow sensor to get the chiller running until the new wire harness arrived the next day. This is the 3-wire cwfs. i have seen the 4-wire sensors that have 24vac powering them up and the other two wires are just a switch, easy to bypass. The 3-wire didn't seem too easy to bypass since it sends a 0-24vdc signal to the mbb.
-
06-09-2012, 04:43 PM #23
-
06-09-2012, 04:52 PM #24
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,511
-
06-09-2012, 04:54 PM #25
Regular Guest
- Join Date
- Sep 2011
- Posts
- 12
See terminal 15B. What is the signal generated by the cwfs.
According to this diagram how could this have been bypassed to allow the chiller to run until a cwfs wire harness could be ordered?
-