    carrier 30hxc
    I have a chiller that's out on the factory flow switch. The red leds are on. Check pumps and water flow all ok but the switch won't close. Is there a way to bypass switch to getthe chiller running.
    East of big city prices.
    It`s pretty easy if you have a FSR in your panel and that`s all I will say.
    Sep 2011
    BAJA AND CALIFORNIA
    send complete model and i will send you the wiring digram and show how to bypass but becarefull to put side protection , not leave the unit without flow switch protection
    Hawaii
    30HXC106RZ550
    The Hot South
    I wouldn't be giving detailed instructions on bypassing a safety if I was you.....especially a flow switch on a chiller with a flooded evaporator.
    Oct 2011
    La.
    these flow swithes are very sensitive to dirty cooling media. check cooling media for dirt and funk on the sensor. the unit checks the status of the switch every startup, so just jumping it will not work but for once. I would err on the side of caution as well, because the building people always forget that they told you to jump out a safety. you only have one reputation, protect it!
    Sep 2011
    BAJA AND CALIFORNIA
    i follow the recommendation of spinning wheel, first clean the sensor of the switch and make test. also your reputation is important
    NE Ohio
    Quote Originally Posted by R123 View Post
    I second that. Never jump it out if you enjoy your job.
    Not in Iran
    Talking
    love the FSR people.,
    i would never just out a flow switch., better to replace than to jump out.,
    OR U MAY BE JUMPING OFF A BRIDGE.,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
    Quote Originally Posted by mlkwal1 View Post
    Yeah dude see you at the party on the bridge. Something's are better less said too much info can mess things up just like too much info will. I would never leave one jumped out but will to verify after checking a PD. Found a ifm stuck closed today.
    Not in Iran
    yep., and that would be the only way
    Oct 2005
    i know carrier is having some problems with those switches...but i would never jump a flow switch..good luck
    RTFM!!!
    Sep 2011
    Quote Originally Posted by ESS CHILL WATER View Post
    I would like to know how to temporary bypass the 3-wire flow sensor for troubleshooting purposes.
    How does the 3-wire sensor operate?
    I understand it has a ground and 24vac going to it, but what does it send back on the wire going to the main board ?