Results 14 to 18 of 18
    Jan 2005
    where it's nice and warm
    When the 052-CAP-TT-HH is too big for your cap tube systems you may use EK-032-SV-CAP made by Emerson.
    Jul 2000
    Guayaquil, EC
    Quote Originally Posted by fridg View Post
    The manufacturer will tell you that a cap tube system is critically charged , they are to some extent but you can cut off up to 200mm on some and be confident that it will still run to design conditions.
    It's true you can cut off a significant length of cap tube and still have good performance, but the key to this is the system charge.
    If you have a system which originally required 16 oz of refrigerant and you shorten the cap tube, it won't perform quite the same if you recharge with that same 16 oz. of refrigerant. A slight adjustment in charge will usually bring it in line.
    For a given system, a shortened cap tube would require a lower amount of liquid subcooling entering the tube...ie, a slightly lower charge.
    Of course, there would a limit as to how much you can snip off.
    Sep 2011
    Plainfield IL
    You know Pascone it sounds like to me your system is contaminated. Sporlan has come out with a new cap tube drier that is suppose to remove particles as small as like 5 micron. I tried one on a contaminated sytem like yours and the cap tube still clogged up in less than 1 year.
    All you can do is uninstall the compressor and dump the oil and repalce it till the cap tubes stop clogging. The particles will be in the oil and in all the piping.
    Tell your customer to buy a new unit or just replace everything! Evap coil piping and condenser unit. Its really all you can do.
    Its happen to me a handfull of times.
    Goodluck Evan
    Feb 2016
    N'awlins Dawlin' USA and Palmares Costa Rica
    old thread but updated link for the Sporlan drier:
    http://sporlanonline.com/literature/40/40-337.pdf
    Sep 2015
    Marlton, NJ
    Copper spun drivers are garbage. Almost all will eventually plug up. When I have a suspected cap tube plugged, I change the driver and usually cut away about 4 -6 inches of the cap tube. Usually this is sufficient as changing the whole cap tube is unnecessary. For severely waxed systems, yeah your gonna have to change the whole tube and if your going through all that then yeah a compressor oil change should be done as well JUST to be sure you never have to go through it again. 134a seems to be the biggest offender. I feel like the cap tube systems that run on r404a hardly ever clog up at all. Maybe the higher pressures?