Results 1 to 7 of 7
  1. #1
    Join Date
    Dec 2007
    Posts
    3,935

    Question Vermont Castings LHEC30RFN

    anyone have a troubleshooting guide or LED decoder other than what is in the install manual?

    got a unit that is shutting down on the customer yet works great while I am there.

    check in the install manual all pass.

    LED is continually blinking every 1.5 - 2 seconds.

    did a complete cleaning and checked and rechecked the MV and Ohms per manual.

    Ideas?

  2. #2
    Join Date
    Dec 2007
    Posts
    3,935
    just clicked on the "Majestic help please" thread and it is the same as this unit.

  3. #3
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    5,450

    Cool just move in

    Sorry, couldn't resist that one.


    I'll see what I can find out. Stay tuned...

  4. #4
    Join Date
    Aug 2011
    Location
    Ontario
    Posts
    372
    More details would be good. When unit does not work for customer does pilot drop out or does burner just not come on ??
    There is no bad beer, some just taste better than others.

  5. #5
    Join Date
    Dec 2007
    Posts
    3,935
    Not the place I want to move into, but thanks.

    This customer is scared of gas, does not even want to look at pilot.

    I will assume it takes everything out, except the fan, as I have had to light the pilot when I get there.

    The first time it shut down was after the local gas company lit it. guy condemned the powerpiles without checking anything. Maybe he is that good.

    Second time, after I did service, it was 2 days later. It was on, by remote with flame and fan on number 2, for 5 minutes max. Customer walked outside and came back within a couple minutes and it was off. He could not get it to come back on by remote, so I assume it shut pilot and main burners down. He did not check.

    Finally got a call from tech support and they gave me a couple other things to check more in depth.

    sounds like powerpile(s) bad or gas valve, but more than likely PP.

  6. #6
    Join Date
    Aug 2011
    Location
    Ontario
    Posts
    372
    You said you can light it and it runs for a while.?? What does flame look like, is it ghosting at all ? if flame is lifting off pilot PP could be venting issues.
    There is no bad beer, some just taste better than others.

  7. #7
    Join Date
    Dec 2007
    Posts
    3,935
    not lifting, flames look normal, blue mostly and yellow tips where it needs to be.

    runs for the time I am there and pilot stays on for X amount of days. customer sets it at 2 of 6 flame, it runs for a bit and went out. I am not sure if this was the only time he tried it.

    tech support said similar, maybe a chimney issue. could be a blockage or cold.

    thanks