I just received this info from Honeywell:

"The MERV rating on F200E1037 is 13. The initial pressure drop is 0.28 in. Wc and the air flow maximum capacity is 2000cfm"

Can I assume this PD is at 2000cfm? I am running about 500cfm, with a .05 in PD on my Merv10 EZ-Flex filter. I would like to upgrade to the Honeywell, but not if it will harm the equipment.