  1. #101
    Join Date
    Mar 2005
    Posts
    1,762
    Post Likes
    Hi guys where as I would almost certainly always agree and follow you trane vets to a Tee , I stand with disabling stand-by circuit and alternating monthly on building controls , with same recommendation of capacity/current limit set way down say 60% as a start. Remember the key * this equipment is so oversized its still short cycling in summer load months, unless theres valve control piping issues , which for now we can assume there isnt. Its still two chillers in a way , (even though I do understand the characteristics that make them common),and I would treat them as such, and enable the standby circuit as needed in case of under capacity, same as you would a completely redundant stand-by chiller, The bad part is he says his controls are very old , who knows how versatile , regards stan
    Keep it simple to keep it cool!

  2. #102
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by stanbyyourword View Post
    Hi guys where as I would almost certainly always agree and follow you trane vets to a Tee , I stand with disabling stand-by circuit and alternating monthly on building controls , with same recommendation of capacity/current limit set way down say 60% as a start. Remember the key * this equipment is so oversized its still short cycling in summer load months, unless theres valve control piping issues , which for now we can assume there isnt. Its still two chillers in a way , (even though I do understand the characteristics that make them common),and I would treat them as such, and enable the standby circuit as needed in case of under capacity, same as you would a completely redundant stand-by chiller, The bad part is he says his controls are very old , who knows how versatile , regards stan
    i understand what you are talking about and it isn't a bad idea. the only problem that i have with it (other than the old BAS controls) is that if 1 circuit trips off-line (for whatever reason), you do not have a back up circuit ready to go. if you trust your BAS to react quickly and correctly, then you have a reasonable idea...i just don't trust BAS guys to understand how to react properly.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  3. #103
    Join Date
    Mar 2005
    Posts
    1,762
    Post Likes
    hi Jay, yes of course , but thats the whole "proper commissioning" thing , i`d say you have to have the run status signals to bms, maybe 1 hr registered run time , controls enable standby ckt. Local chiller controls will stage this ckt as normal if rqu`d. And if alarm signal sent , instantly enable other ckt , Its good to have extra capacity of course, but has to setup correctly , eg chiller cycling the unloaders to death , stan
    Keep it simple to keep it cool!

  4. #104
    Join Date
    Nov 2011
    Location
    South Texas
    Posts
    84
    Post Likes
    Thread Starter
    Unfortunately the BAS system in this building still has a taradactyl that flies from the server room to the chiller to hit start and stop. I'm in the process of getting a bid together to update to a brand new BAS system.

  5. #105
    Join Date
    Mar 2005
    Posts
    1,762
    Post Likes
    now you have some recommendations on how to control it, good luck stan
    Keep it simple to keep it cool!

  6. #106
    Join Date
    Nov 2011
    Location
    South Texas
    Posts
    84
    Post Likes
    Thread Starter
    Sorry forgot to post a update. We went ahead and replaced the slide valves in both units and the load unload solenoids and actuators and all is well. She has been running like a top since the repairs were performed.

  7. Likes Bklyntek liked this post.
  8. #107
    Join Date
    Apr 2012
    Location
    So.Fl. & NYC
    Posts
    201
    Post Likes
    Gentleman,I love this post and Stan while it's been a few years. I hope all is well with you and your family. Awesome display of collaborative efforts and truly sound diagnostic procedures. Just awesome....

  9. Likes stanbyyourword liked this post.
  10. #108
    Join Date
    Mar 2005
    Posts
    1,762
    Post Likes
    Hope you are well too! yes it was a good thread! Im rarely so talkative on here all the best stan
    Keep it simple to keep it cool!

+ Reply to Thread
Page 6 of 6 FirstFirst 123456

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •