01-08-2012, 04:58 PM
#101
Hi guys where as I would almost certainly always agree and follow you trane vets to a Tee , I stand with disabling stand-by circuit and alternating monthly on building controls , with same recommendation of capacity/current limit set way down say 60% as a start. Remember the key * this equipment is so oversized its still short cycling in summer load months, unless theres valve control piping issues , which for now we can assume there isnt. Its still two chillers in a way , (even though I do understand the characteristics that make them common),and I would treat them as such, and enable the standby circuit as needed in case of under capacity, same as you would a completely redundant stand-by chiller, The bad part is he says his controls are very old , who knows how versatile , regards stan
Keep it simple to keep it cool!
-
-
01-08-2012, 10:41 PM
#102
Originally Posted by
stanbyyourword
Hi guys where as I would almost certainly always agree and follow you trane vets to a Tee , I stand with disabling stand-by circuit and alternating monthly on building controls , with same recommendation of capacity/current limit set way down say 60% as a start. Remember the key * this equipment is so oversized its still short cycling in summer load months, unless theres valve control piping issues , which for now we can assume there isnt. Its still two chillers in a way , (even though I do understand the characteristics that make them common),and I would treat them as such, and enable the standby circuit as needed in case of under capacity, same as you would a completely redundant stand-by chiller, The bad part is he says his controls are very old , who knows how versatile , regards stan
i understand what you are talking about and it isn't a bad idea. the only problem that i have with it (other than the old BAS controls) is that if 1 circuit trips off-line (for whatever reason), you do not have a back up circuit ready to go. if you trust your BAS to react quickly and correctly, then you have a reasonable idea...i just don't trust BAS guys to understand how to react properly.
"Right" is not the same as "Wise".
Don't step on my favorite part of the Constitution just to point out your favorite part.
Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.
-
01-08-2012, 10:48 PM
#103
hi Jay, yes of course , but thats the whole "proper commissioning" thing , i`d say you have to have the run status signals to bms, maybe 1 hr registered run time , controls enable standby ckt. Local chiller controls will stage this ckt as normal if rqu`d. And if alarm signal sent , instantly enable other ckt , Its good to have extra capacity of course, but has to setup correctly , eg chiller cycling the unloaders to death , stan
Keep it simple to keep it cool!
-
01-09-2012, 01:08 AM
#104
Unfortunately the BAS system in this building still has a taradactyl that flies from the server room to the chiller to hit start and stop. I'm in the process of getting a bid together to update to a brand new BAS system.
-
01-09-2012, 01:18 AM
#105
now you have some recommendations on how to control it, good luck stan
Keep it simple to keep it cool!
-
10-18-2012, 09:23 PM
#106
Sorry forgot to post a update. We went ahead and replaced the slide valves in both units and the load unload solenoids and actuators and all is well. She has been running like a top since the repairs were performed.
-
Post Likes - 1 Likes, 0 Dislikes
-
10-01-2015, 07:18 PM
#107
Gentleman,I love this post and Stan while it's been a few years. I hope all is well with you and your family. Awesome display of collaborative efforts and truly sound diagnostic procedures. Just awesome....
-
Post Likes - 1 Likes, 0 Dislikes
-
10-02-2015, 01:19 AM
#108
Hope you are well too! yes it was a good thread! Im rarely so talkative on here all the best stan
Keep it simple to keep it cool!