Trane RTAA 215// circuit a,b intermittent low oil flow codes 199
I have read and lurked here for a while before posting for help. Background on the unit is 220 ton chiller system 1998 vintage with dual screws. The unit is intermittently shutting down either circuit A or B from time to time with no rhyme or reason and it never acts up while I'm onsite to catch it. Right now it's 83 degrees here and dropping to 60 or so at night. Sometimes it will go for days perfectly without a problem.
All condenser fans are running correctly operation verified
25lb of pressure drop across both circuit oil filters
UCM has updated program and OAT sensor installed
Oil level is spot on in both oil coolers
All electrical connections on oil DP switch have been verified
Compressors are starting at 40% load and then modulating up to around 70%
Condenser is visibly clean but I'm going to wash it out tomorrow to get a baseline on it.
I have not physically tested the oil pressure DP switch's yet.
But when it was 112-114 degrees this summer it ran like a top without a problem it's only once the weather cooled off in the last month these stinkin little gremlins are showing up. thanks for the help and any ideas are appreciated.
-
11-07-2011, 07:48 PM #2
I would start w the DP switch., oil filter., clean condenser coils., and charge.,
good luckno signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
11-07-2011, 08:08 PM #3
Professional Member*
- Join Date
- Dec 2008
- Location
- Dixiana, AL
- Posts
- 2,487
If you had gone ahead and done these two things, it probably wouldn't have PO'ed graham for you to start this thread. As it is, he's probably choking on his beer right now and trembling too hard to type in his response.
I'd get these two items out of the way before doing anything else. Post your actual numbers on everything if you have to call back........
You can also find endless hours of reading on this subject and all of it's nuances simply by doing a site search on it.
-
11-07-2011, 09:07 PM #4
Regular Guest
- Join Date
- Nov 2011
- Location
- South Texas
- Posts
- 60
10-4 I'll wash it and post up some numbers tomorrow. Thanks for the help.
-
11-07-2011, 09:27 PM #5
AAAaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaa aaaaaaaaahhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhh hhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhh
f%%%%%%%%%%%########$$$$$$$$$$**********&&&&&&&&&& &???????????????? not anothing friggin RTAA oil code post .!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!!
AAaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaa
Wheres my gattling gun Im goin Postal !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
11-07-2011, 09:50 PM #6
Regular Guest
- Join Date
- Nov 2011
- Location
- South Texas
- Posts
- 60
How does the UCM logic work regarding this safety. While running it is looking for a minimum 50 lb differential and the contacts are closed. Does it test the integrity of the circuit in any other manner during operation and or shutdown process.
I don't have a clue what conditions are present when the failure is actually happening to determine if it is during system run or start up or some combination between.
Sure would be nice if it had freeze frame diagnostics like car control systems do.
-
11-07-2011, 10:23 PM #7
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 877
All the UCM is doing, regarding this fault, is look at the DP switch contacts. If it opens, it calles out the fault. The DP switch should be set at 50 PSID + or - 5 (i set it at 55). Upon shutdown, the UCM closes the master oil solenoid valve and looks for the DP switch to open to test the integrity of the switch.
-
11-07-2011, 10:32 PM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
11-07-2011, 10:53 PM #9
Regular Guest
- Join Date
- Nov 2011
- Location
- South Texas
- Posts
- 60
Everything about it looks stone stock. We'll give it a good bath and scrub behind the ears double check the pressure switch's and see what happens. I had a hunch I just wanted to hear someone else's opinions to back up my hunch. Thanks again.
-
11-07-2011, 10:30 PM #10
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
11-08-2011, 12:52 AM #11
'WAS' is right! now Graham is the nicest Trane guy!
check your oil pressure switch 'X' number...if it ends in '03' or '-03'...change it out as they tended to drift over time.
perform a very thorough checkout of the oil solenoid coil. if it is overheating or occasionally dropping out (bad wire nuts?) then this will cause the pressure switch to trip and of course, check out the pressure switch.
the foaming around Grahams mouth isn't from the beer!The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
11-08-2011, 06:14 AM #12
-
11-08-2011, 07:42 PM #13
Ah what will we all do when all the AA's have passed into the twilight now that Trane has moved on to AC's! It's fun to watch or at least read these responses!
And I have learned alot reading them between the laughs!!I'm good at making things cold...You can ask my first two wives!


Reply With Quote