    I have read and lurked here for a while before posting for help. Background on the unit is 220 ton chiller system 1998 vintage with dual screws. The unit is intermittently shutting down either circuit A or B from time to time with no rhyme or reason and it never acts up while I'm onsite to catch it. Right now it's 83 degrees here and dropping to 60 or so at night. Sometimes it will go for days perfectly without a problem.
    All condenser fans are running correctly operation verified
    25lb of pressure drop across both circuit oil filters
    UCM has updated program and OAT sensor installed
    Oil level is spot on in both oil coolers
    All electrical connections on oil DP switch have been verified
    Compressors are starting at 40% load and then modulating up to around 70%
    Condenser is visibly clean but I'm going to wash it out tomorrow to get a baseline on it.
    I have not physically tested the oil pressure DP switch's yet.
    But when it was 112-114 degrees this summer it ran like a top without a problem it's only once the weather cooled off in the last month these stinkin little gremlins are showing up. thanks for the help and any ideas are appreciated.
    Not in Iran
    I would start w the DP switch., oil filter., clean condenser coils., and charge.,
    good luck
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
    Dec 2008
    Dixiana, AL
    Quote Originally Posted by aggiechillertech View Post
    If you had gone ahead and done these two things, it probably wouldn't have PO'ed graham for you to start this thread. As it is, he's probably choking on his beer right now and trembling too hard to type in his response.
    I'd get these two items out of the way before doing anything else. Post your actual numbers on everything if you have to call back........
    You can also find endless hours of reading on this subject and all of it's nuances simply by doing a site search on it.
    Nov 2011
    South Texas
    10-4 I'll wash it and post up some numbers tomorrow. Thanks for the help.
    ottawa canada
    AAAaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaa aaaaaaaaahhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhh hhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhh
    f%%%%%%%%%%%########$$$$$$$$$$**********&&&&&&&&&& &???????????????? not anothing friggin RTAA oil code post .!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!!
    Wheres my gattling gun Im goin Postal !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
    Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!
    Nov 2011
    South Texas
    How does the UCM logic work regarding this safety. While running it is looking for a minimum 50 lb differential and the contacts are closed. Does it test the integrity of the circuit in any other manner during operation and or shutdown process.
    I don't have a clue what conditions are present when the failure is actually happening to determine if it is during system run or start up or some combination between.
    Sure would be nice if it had freeze frame diagnostics like car control systems do.
    The Hot South
    All the UCM is doing, regarding this fault, is look at the DP switch contacts. If it opens, it calles out the fault. The DP switch should be set at 50 PSID + or - 5 (i set it at 55). Upon shutdown, the UCM closes the master oil solenoid valve and looks for the DP switch to open to test the integrity of the switch.
    Dallas ,Texas
    Quote Originally Posted by R123 View Post
    I`m wanting to say I heard that there was a bad batch of switches out there. Not sure how old this machine is or if it has ever had the problem addressed.
    UA 100
    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
    Nov 2011
    South Texas
    Everything about it looks stone stock. We'll give it a good bath and scrub behind the ears double check the pressure switch's and see what happens. I had a hunch I just wanted to hear someone else's opinions to back up my hunch. Thanks again.
    Dallas ,Texas
    You might want to use the search feature there are several threads already covering the subject of oil pressure alarms. Maybe Jayguy will show up and see your thread, he doesn`t go postal all the time like Graham he was the nicer Trane guy.
    UA 100
    Quote Originally Posted by thegoodlistener View Post
    ...Maybe Jayguy will show up and see your thread, he doesn`t go postal all the time like Graham he was the nicer Trane guy.
    'WAS' is right! now Graham is the nicest Trane guy!
    check your oil pressure switch 'X' number...if it ends in '03' or '-03'...change it out as they tended to drift over time.
    perform a very thorough checkout of the oil solenoid coil. if it is overheating or occasionally dropping out (bad wire nuts?) then this will cause the pressure switch to trip and of course, check out the pressure switch.
    the foaming around Grahams mouth isn't from the beer!
    The weak aren't destroyed by the strong.
    The weak are destroyed by the under-estimated.
    I know a famous song that ends in 'my nose'. The artist is dead. Know who?
    ottawa canada
    Quote Originally Posted by jayguy View Post
    Dec 2009
    Southern US
    Ah what will we all do when all the AA's have passed into the twilight now that Trane has moved on to AC's! It's fun to watch or at least read these responses!
    And I have learned alot reading them between the laughs!!
    I'm good at making things cold...You can ask my first two wives!