Thread: Cold Start Boiler

  1. #1
    Join Date
    Sep 2005
    Posts
    73
    Post Likes
    Here is a question I have.

    I have a WM Ultra 230. On average, it takes about 5 minutes to reach the set point for the water temp from a cold start. I am just trying to figure out if that is normal or too long?

  2. #2
    Join Date
    Oct 2005
    Posts
    927
    Post Likes

    Use

    What are you using this for?

  3. #3
    Join Date
    Sep 2005
    Posts
    73
    Post Likes
    Thread Starter
    Both space heating and DHW. Unit feeds a coil in a variable speed air handlder. DHW is a ultra plus 60.

  4. #4
    Join Date
    Oct 2005
    Posts
    927
    Post Likes

    Do you think this is long or two short

    What are the settings and outside temp?

  5. #5
    Join Date
    Oct 2005
    Posts
    927
    Post Likes

    High low set points

    What are your settings and what is the outside temperature. Five min at this point does not sound bad?

  6. #6
    Join Date
    Sep 2005
    Posts
    73
    Post Likes
    Thread Starter
    Ranges are as follows: 70 degree ODT = 140 degree water, 20 degree ODT = 180 degree water. Usuallay the cold start is around 110 degrees and takes about 4-5 minutes to get to 156 degrees.

  7. #7
    Join Date
    Oct 2005
    Posts
    927
    Post Likes

    Fourty six

    More then ten degrees a min I would think that is good

  8. #8
    Join Date
    Oct 2005
    Posts
    927
    Post Likes

    fourty six

    11.5 degrees per minute or 9.2 degrees per minute sounds ok from what you have said 46 degrees 4-5 min sounds reasonable even nice from a cold idling start up.

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    For heat, it sounds alittle over sized. But that could be low flow through the hydro coil, or you have your cfm set low.

    The 230 can modulate down to 46,000btu input. And hydro's don't hold alot of water, so you get a quick temp rise.

    If the temp rises too fast, the Ultra will lock out and give you a code 30.


  10. #10
    Join Date
    Sep 2005
    Posts
    73
    Post Likes
    Thread Starter
    Have not had that problem. I lowered the blower speed on the ultra and changed the off differential to 16 degrees, this stopped all short cycling of the boiler and it runs like a charm know. The boiler will stay fired and not short cycle for an entire heat call how ever long it may be.

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Cool.

    Do you have the Control Addendum instructions.

  12. #12
    Join Date
    Sep 2005
    Posts
    73
    Post Likes
    Thread Starter
    Yes, that is where I learned to make all of the adjustments.

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Kinda though you did, since none of those settings is in the normal control instructions.

    Without giving step by step instructions.

    You know that setting that says don't set below 140.

    Set it to 130, as long as you don't change the other setting, your DHW won't lag.

    I have some as low as 120, on 40 gal indirects.


    PS: If you have 0011 circs, and they fail under warranty, ask your installer about switching to 0014 circs under warranty.

  14. #14
    Join Date
    Sep 2005
    Posts
    73
    Post Likes
    Thread Starter
    Cool,

    I set it to 130 that way I could set the off diferential 10 16 degrees on the DHW as well to avoid short cycling. I works great as well.

  15. #15
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Let me know if you have any DHW problems with it set that way.

  16. #16
    Join Date
    Sep 2005
    Posts
    73
    Post Likes
    Thread Starter
    Sorry for the confusion, I have had it set that way for about a month now and there is absolutelt no difference to me....

  17. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Cool.

    I haven't had any complaints about it from anyone yet. Some as long as four years.

    If you haven't had any trouble in a month, its doutbfull you will, unless your hot water usage would go way up, or you inlet water temp drops to 30.

  18. #18
    Join Date
    Sep 2005
    Posts
    73
    Post Likes
    Thread Starter
    Originally posted by beenthere
    Kinda though you did, since none of those settings is in the normal control instructions.

    Without giving step by step instructions.

    You know that setting that says don't set below 140.

    Set it to 130, as long as you don't change the other setting, your DHW won't lag.

    I have some as low as 120, on 40 gal indirects.


    PS: If you have 0011 circs, and they fail under warranty, ask your installer about switching to 0014 circs under warranty.
    Why the change from a 0011 to a 0014?

  19. #19
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Apparently they have been having trouble with the 0011 some times.

    All 155, 230, and 310'come with 0014's now.
    With a note, where ever the manual recommends a 0011, use a 0014 instead. This includes indirects hooked to Ultra's.


Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •