    Here is a question I have.
    I have a WM Ultra 230. On average, it takes about 5 minutes to reach the set point for the water temp from a cold start. I am just trying to figure out if that is normal or too long?
    Oct 2005
    Use
    What are you using this for?
    Both space heating and DHW. Unit feeds a coil in a variable speed air handlder. DHW is a ultra plus 60.
    Oct 2005
    Do you think this is long or two short
    What are the settings and outside temp?
    Oct 2005
    High low set points
    What are your settings and what is the outside temperature. Five min at this point does not sound bad?
    Ranges are as follows: 70 degree ODT = 140 degree water, 20 degree ODT = 180 degree water. Usuallay the cold start is around 110 degrees and takes about 4-5 minutes to get to 156 degrees.
    Oct 2005
    Fourty six
    More then ten degrees a min I would think that is good
    Oct 2005
    fourty six
    11.5 degrees per minute or 9.2 degrees per minute sounds ok from what you have said 46 degrees 4-5 min sounds reasonable even nice from a cold idling start up.
    For heat, it sounds alittle over sized. But that could be low flow through the hydro coil, or you have your cfm set low.
    The 230 can modulate down to 46,000btu input. And hydro's don't hold alot of water, so you get a quick temp rise.
    If the temp rises too fast, the Ultra will lock out and give you a code 30.
    Have not had that problem. I lowered the blower speed on the ultra and changed the off differential to 16 degrees, this stopped all short cycling of the boiler and it runs like a charm know. The boiler will stay fired and not short cycle for an entire heat call how ever long it may be.
    Cool.
    Do you have the Control Addendum instructions.
    Yes, that is where I learned to make all of the adjustments.
    Kinda though you did, since none of those settings is in the normal control instructions.
    Without giving step by step instructions.
    You know that setting that says don't set below 140.
    Set it to 130, as long as you don't change the other setting, your DHW won't lag.
    I have some as low as 120, on 40 gal indirects.
    PS: If you have 0011 circs, and they fail under warranty, ask your installer about switching to 0014 circs under warranty.