Results 1 to 13 of 20
    Aug 2011
    Carrier 19xr teardown interval
    Have a carrier 19xr with 29,000 hours. At what interval is a teardown recomended?
    Jun 2008
    Windsor, Ont.
    We usually go with "If it ain't broke don't fix it". If it runs good and regular oil sample testing is not producing anything of concern just ler her run. We have several machines with over 50,000 hrs on them and never been apart. The last 19XL we did was at 48,000 hrs when the oil sample turned up with high tin content and led to new bearings throughout.
    Oct 2011
    La.
    hours are important, but the type of hours are more important. does the unit surge often, "poor tower conditions", start and stop alot. these are the questions that you need to ask yourself. a little preventative maintenance is worth the money spent.
    Apr 2005
    20,000 if unit has run under low load condition for long periods ...take oil sample from oil filter.
    Sep 2011
    BAJA AND CALIFORNIA
    The Carrier Corporation recommends a “high Speed” assembly inspection (ST-3) every 10,000 to 13,000 hours of operation. For machines that have 20,000 to 22,000 hours of operation. The Carrier Corporation recommends a complete major inspection (ST-6). This includes the (ST-1) annual maintenance, the same “high speed” assembly inspection as in the ST-3 Plus transmission bearings and gears inspection.
    hope help you also we recommend oil sample in a yearly basis plus vibration analisis
    Jan 2006
    Quote Originally Posted by ESS CHILL WATER View Post
    Thank you your post, would you like to let me know that where can I find the above documents?
    Can
    Sep 2011
    BAJA AND CALIFORNIA
    Hi Can share with you the complete scope of work for ST1 , ST3 , ST6 this particular code we handling internal when i just work for the factory , let me check with my papers and certanly can share with you .
    regards
    Oscar
    Jan 2006
    Dear ESS Chill Water,
    Thank you for your reply, I'm working for repair and T & C of the Carrier centrifugal chiller from 1987 up to now. I know that how long time need to inspec the hi-speed and overhaul the compressor. But never find any document to support us to recommend the customer to do the above work. Hope that you can send me a copy of ST1, ST3 and ST6 by email.
    Thank you and best regards!
    Can
    Sep 2011
    BAJA AND CALIFORNIA
    Dear CAN
    for the vintage of the unit that you going to overhaul must be a 19DG,DK,DM, or may ve a big unit 19C or 17FA ??? can you send me the model of the unit may be change the time of inspections , the unit also may work with R-11 or retrofit to R-123 ????? as soon as you send me the info i will check my files and share with you , also internal bulletins.
    regards
    Oscar
    Jan 2006
    I'm talking the documents for the 19XL, 19XR, 19EX, 17EX and 17FA.
    Can
    Sep 2011
    BAJA AND CALIFORNIA
    K CAN LET ME CHECK AND I WILL FEED BACK
    REGARDS
    OSCAR
    P.S PLEASE PROVIDE ME YOUR EMAIL
    Jan 2006
    REGARDS
    OSCAR
    southeng@biznetvigator.com
    Can
    Oct 2011
    Upstate NY
    I agree with nyrb... Oil analysis a my indicator
