Thread: Ruud Mod vs. Bryant 2-stage, Contractor 1 vs. 2

  1. #1
    Join Date
    Jan 2006
    Location
    Minneapolis, MN
    Posts
    70
    Post Likes
    I am throwing this question out to this forum. (Thanks in advance!)

    I live in Minnesota (I can give more detials on the size of house, etc., if this is relevant). I am in the process of getting bids to replace furnace and AC. Also an issue I'd like to address is a problem of keeping our basement warm in winter.

    Contarctor 1: Fantastic referrals, very service-oriented, big company (75 years in business). Rep spent 2+ hours looking at system, looking at home (e.g., counting vents and returns on each floor), asking about concerns. Will do a heat calculation to confirm sizing. Proposed Bryant 90i (two-stage) with Puron AC (Model 550A, 13 SEER).

    Contractor 2: Small company (but over 20 years old), very low-key (perhaps because sales rep was on vacation, so a service tech came out). Rep quickly looked at existing furnace and AC, proposed replacing with same rated units, was through in under 30 minutes. Will bid a Ruud Modulating 90+ (and will also price the 2-stage at my request) and an R-22, 13-SEER AC unit (said he didn't trust the Puron units and that there would be no problems servicing R-22 into the future).

    As an engineer, I am enthralled with the modulating furnace. Seems perfect fo the frigid north. However, Contractor 1 (Bryant) seems to be willing to make sure they do everything right. Everyone says the installation is more imprtant than the unit... Also concerned about R-22 AC; would a repair 15 years out be insanely expensive?

    Please, your opinions. Go with one of these? Get more bids? Thanks, again!

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Simply put; there is no actual comparison to the Rheem/Ruud modulating furnace. It is in a catagory all by itself.

    That does not make it a worth the cost benefit in all situations however. I like to refer to the mod as a freak of the industry, because it is not a furnace that I have a comparable model to do battle against But again; just because the mod has specific advantages does not mean it is going to be a noticeable difference in comfort.

    The other issue is that the mod furnace must be installed in a very particular manner and must use the fuzzy logic thermostat and controls in order to make it at all beneficial. I have seen and heard of more mods installed in a way that they are no more beneficial than a single or two stage furnace then those that are properly installed and set up.

    For extreme comfort in a home with problematic thermal/stratification issues, nothing on the market can compare to a properly installed and set up mod furnace.

    As for the service tech rather then a sales rep doing the quote; I have more confidence in the guy who has to work on equipment then the guy whose only connection to the equipment is his commision check.
    Training is important!
    Practical Training is a must!

  3. #3
    Join Date
    Jun 2005
    Posts
    347
    Post Likes
    It’s hard to say what the future will bring. The equipment manufactures are not making the stuff with r-22 in it. Doesn’t mean there won’t be r-22 to put in it. I personally would get at least one more bid, for similar equipment. Then decide on which company will do the best job for a fair price. My company is usually the highest priced company out but we sell more jobs a year than competitors on quality of work, service after the sale, reliability.

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    R22 equipment can be made until 2010. That's 4 long years, so yes, equipment manufacturers ARE making goodies with R22 in it. R22 will be available new until 2020 and longer in recovered form plus there are new gases that work in place of R22 out now. One has a newer version coming soon, don't know the details.

    If I were doing it, I'd go R22 myself.

    As for sizing, looks like neither did any heat gain/loss calc. Counting registers doesn't tell much.

  5. #5
    Join Date
    Jan 2006
    Location
    Minneapolis, MN
    Posts
    70
    Post Likes
    Thread Starter
    Originally posted by RoBoTeq
    But again; just because the mod has specific advantages does not mean it is going to be a noticeable difference in comfort.

    The other issue is that the mod furnace must be installed in a very particular manner and must use the fuzzy logic thermostat and controls in order to make it at all beneficial. I have seen and heard of more mods installed in a way that they are no more beneficial than a single or two stage furnace then those that are properly installed and set up.
    So how do I assess whether this company can set up this great piece of equipment properly? Call the owner and grill him with any particular questions?

    I could call another Ruud or Rheem contractor for another bid, but it is hard to know whom to call...

  6. #6
    Join Date
    Jan 2004
    Location
    Here and there
    Posts
    4,812
    Post Likes
    As robo says go fot the best folks to install it !!!! My mod will only do as well as it is installed. His goodman can do better if set up right
    i belong to peta ... people eating tasty animals. all my opinions are just mine.

  7. #7
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    With the mod, and there are others here who are more up on this furnace then I am now, I would ask if the thermostat that is required for full modulating efficiency is being quoted as well as subtleties like; Where in the duct will you be locating the "leaving air sensor". Questions like these will let the quoting contractor know you are learning about this system and will require it be installed properly.

    The other side of this issue is this; will you noticeably benefit from a mod furnace or do you just want the neat technology? If the latter, I can understand and appreciate
    Training is important!
    Practical Training is a must!

  8. #8
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    contractor #2 inexperienced. most of your advanced contractors have already moved toward r410 systems. also contactor #2 will be the first to down grade every engineered advancement in a/c mostly becuase most residential companys like simplicity over and above anything else. they will tell you r410 a is no good, zoning system are not very reliable and so forth which are false statements.
    bryant system is a better quality system than ruud. i would go back to contractor 1 and get him to bid you modulating furnace which is probably better known as a variable speed gas furnace.

  9. #9
    Join Date
    Jan 2006
    Location
    Minneapolis, MN
    Posts
    70
    Post Likes
    Thread Starter
    Originally posted by RoBoTeq
    The other side of this issue is this; will you noticeably benefit from a mod furnace or do you just want the neat technology? If the latter, I can understand and appreciate
    Of course, I am enamored with the technology, but I do think my home will benefit. We have a two-story with a finished, walk-out basement. The vents in the basement run through the slab, under the floor (transit heating?). Even if we run the fan continuously, the basement stays 5-10 degrees cooler. One theory is that the furnace on-off cycle is too short to heat up the vent run under the slab, so not enough heat is delivered. Under these conditions, the modulating furnace should benefit comfort. Do you agree?

    P.S. I'd rather solve this problem simply and inexpensively, rather than, say, retrofitting a zone system or installing a separate furnace for the basement.

    Thanks for the suggestions, I'll get a list of questions together to ask about the install. Since you seem to be a Rheem/Ruud guy, what do you think of the AC choice? I see they do make the new AC units with R-410A.

    [Edited by jeff-4 on 01-28-2006 at 05:44 PM]

  10. #10
    Join Date
    Jan 2006
    Location
    Minneapolis, MN
    Posts
    70
    Post Likes
    Thread Starter
    Originally posted by airworx
    bryant system is a better quality system than ruud. i would go back to contractor 1 and get him to bid you modulating furnace which is probably better known as a variable speed gas furnace.
    Thanks for your opinion! The Bryant unit is their top-of-the-line, variable fan furnace but only two-stage heating, not fully modulating.

    I'd really like to hear a Bryant person tout their product's advantages...

  11. #11
    Join Date
    Jan 2006
    Posts
    46
    Post Likes
    What is the difference between a fully modulating furnace a variable speed, two stage furnace?

  12. #12
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Jeff, from what you are describing as to the conditions of your home, I agree that the mod furnace...properly set up with the proper thermostat...will benefit you from a comfort standpoint.

    I used to rep Rheem/Ruud but have been repping for another brand for the past six years. I was on board with Rheem/Ruud as a contractor when the mod was first made available and installed the first one in Maryland. I think it is a great furnace (for a freak ) and the closest thing to a perfect furnace in that it will operate at the lowest possible heat and blower speed nearly constantly to keep your home comfy without having to cycle on and off.

    As for the Bryant comments, I have nothing against Bryant, but not only is Bryant no better then any other comparable furnace on the market, Bryand has nothing to compare with the Rheem/Ruud mod. Then there is the matter of Bryant still using the clam shell heat exchanger.
    Training is important!
    Practical Training is a must!

  13. #13
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    This chart shows the heat loss of the house as it gets colder out. It also shows the output of a 2 stage furnace, in this case a Bryant/Carrier 355/MVP. The 3rd line shows the output of a Mod going from 40% when it will cycle to 100% on the coldest day. The output of the Mod nearly perfectly follows the needs of the house. No feeling warm as the furnace runs and cold when it cycles off. Just perfect, steady warmth, like a car heater can do. Only this is automatic.

    I'm not afraid of R410a, like many I am used to R22 and see no reason at this point not to stay with it. Rheem/Ruud certainly has R410a machines available if someone desires. Most brands still have many more R22 units out.


  14. #14
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,307
    Post Likes
    How big is your home? What BTU was quoted to you on both brands?

    I'd go with the Mod, hands down.. They are the best equipement out there, and no one else in the forced air can match the comfort.

    You can down load a home owner's version of the loac calc (red tab on top of screen) for $50.

    With the mod running steady and slow, it will help with your basement set up.

    I would put a mod in my home if there was a Rheem/Ruud dealer in my area. so I went with a Trane XV90 instead.

  15. #15
    Join Date
    Jan 2006
    Location
    Minneapolis, MN
    Posts
    70
    Post Likes
    Thread Starter
    Originally posted by mayguy
    How big is your home? What BTU was quoted to you on both brands?

    I'd go with the Mod, hands down.. They are the best equipement out there, and no one else in the forced air can match the comfort.

    You can down load a home owner's version of the loac calc (red tab on top of screen) for $50.

    With the mod running steady and slow, it will help with your basement set up.

    I would put a mod in my home if there was a Rheem/Ruud dealer in my area. so I went with a Trane XV90 instead.
    Thanks for all of the posts on my questions. They are very helpful!

    I am concerned about sizing, so I tried some of my own sizing calcs. I own a Mac (see, I am enamored by technology), which makes used of HVAC-Calc a bit problematic. So, I tried a shareware program called Easy A/C 2.0. Here are some of the inputs for my home (sorry about the length of this post!).

    Floorspace
    Basement: 1233 sq. ft. (carpeted, I think slab is insulated for transit heat)
    Floor 1: 1232 sq. ft.
    Floor 2: 720 sq. ft.

    Window area (all windows casement, double-paned, low-e, argon filled)
    North: 20 sq. ft.
    South: 22 sq. ft.
    East-West: 217 sq. ft.

    Perimeter walls (8 ft ceilings)
    Basement: 149 ft. (about 1/2 below grade)
    Floor 1: 149 ft.
    Floor 2: 109 ft.

    3 exterior doors, metal, insulated w/storms (excluding 2 French doors that are counted as windows above)
    6.5' x (32", 36", 36")

    2x6 construction, R-19 Walls (Basement wall insulated, 2x4, R-11?)
    10" fiberglass insulation, R-30 Attic

    25 degreee AC design delta temp (95-100 F is usually our max temp in summer; we keep the stat at 76)
    95 degreee AC design delta temp (-25 F is usually attained in our winters, but not this one, yet... We keep the stat at 68 day/55 night.)

    4 people living in house.

    So, with all this, the program calculated 2.6 tons AC and 60350 BTU heating (assuming I input these parameters correctly, which may be a big assumption! There was a part of the program for Floor, Basement, and Slab inputs that was confusing and could have a big impact on the calculations... Hey, do you want to check the answer for me using HVAC-Calc? ). The current AC is 3 tons; current furnace is 80,000 BTU (stated 97% efficiency on furnace). Both bids use 3 tons AC. The Bryant bid is for an 80,000 BTU unit, while the Ruud Modulating furnace is 70,000.

    Whew! Thanks for your patience!

    P.S. I was up for a late-night snack to edit this post. (Hey, I'm an engineer and I'm anal.) Drives my wife crazy. Below is specific calculation output:

    Design TD Cooling 25 Degrees Heat 95 Degrees

    Windows 17914 BTU's 22533 BTU's

    Doors 258.98 BTU's 2364.6 BTU's

    Walls 3082.62 BTU's 12025.65 BTU's

    Ceiling &
    Floors 4068.9 BTU's 16522.2 BTU's

    InFiltration &
    Ventilation 1775.52 BTU's 6904.8 BTU's

    Internal/
    Duct Gain 2400 BTU's 0 BTU's

    Latent 2082.6368 BTU's

    Relative Humidity 55 %

    Total 31582.6568 BTU's / 2.6318881 Tons Heat 60350.25 BTU's

    [Edited by jeff-4 on 01-29-2006 at 03:33 AM]

  16. #16
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,307
    Post Likes
    Wow, you were up late for the "Midnight snack".. Anyway, I own a Mac now, so I am unable to use the HVAC Calc anymore :-(

    Anyway, I was thinking you may need 3 tons cooling, and 60,000 heat, and you figures shows what you need.


    With your current system. did it do well with the heating of the cold snap we had last year. (Where is it this year? LOL odd winter we are having), and A/C kept up with the warm summer we had last year?

  17. #17
    Join Date
    Jan 2006
    Location
    Minneapolis, MN
    Posts
    70
    Post Likes
    Thread Starter
    Originally posted by mayguy
    Wow, you were up late for the "Midnight snack".. Anyway, I own a Mac now, so I am unable to use the HVAC Calc anymore :-(

    Anyway, I was thinking you may need 3 tons cooling, and 60,000 heat, and you figures shows what you need.


    With your current system. did it do well with the heating of the cold snap we had last year. (Where is it this year? LOL odd winter we are having), and A/C kept up with the warm summer we had last year?
    We've never had any problems with either the heating or cooling system keeping up. I remember the cold snap of 1998?, when we hit -35 in the Twin Cities, and the furnace was running almost continuously (but house was fine). The only time the AC has not kept up was on a few hot days some years back when Excel Energy (formally NSP) was cycling our AC via their power saver switch. Then, the house fell off maybe 2 degrees from the setpoint over the day.

    Anyhow, I feel reasonably comfortable with the sizing of these units. I just wish I could find a Rheem/Ruud dealer who would blow me away with their obvious technical expertise and level of service. I'm willing to pay for these attributes!

  18. #18
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Looking at the Rheem & Ruud sites, there are plenty of dealers in the area. None looked familiar to me but I left there 15 years ago and didn't know many small ones. Can't help but think one of them will impress you. The friend I worked for way back when sold Ruud but he's out of it now.

  19. #19
    Join Date
    Jan 2006
    Location
    Minneapolis, MN
    Posts
    70
    Post Likes
    Thread Starter
    Originally, I called one outfit on a Friday afternoon. They promised to call me back on Monday but did not (in fact, haven't heard a peep from them). Maybe I'm too sensitive, but this really annoyed me ! After all, I explaned that I needed my whole system replaced, so I'd think they be right after me for such a large job.

    Of course, the secretary might have misplaced the slip, etc. Should I call them back or go elsewhere? (This is the outfit recommended to me by the Rheem equipment distributor and is just down the road from me.) Seeing how I am really impressed by the Rheem/Ruud equipment, I'd also like to be similarly impressed by the contractor.

    P.S. Thanks for responding to all of my ramblings...

    [Edited by jeff-4 on 01-29-2006 at 03:51 PM]

  20. #20
    Join Date
    Oct 2003
    Posts
    201
    Post Likes
    Look strongly at the bryant evolution system. The 2 stage system. It will react very well with the different temperatures during the winter and the a/c will do the best job with dehumidification during the summer. The evolution control is able to do more as far as comfort is concerned than any other control can.

    T

Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •