    Can Manual J be used to size up a radiant floor system?

  2. #2
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,481
    Post Likes
    Manual J tells you the heat loss/gain for an area, and this info can be used to size any heating/cooling system.
    If everything was always done "by the book"....the book would never change.

  3. #3
    Join Date
    Sep 2002
    Posts
    3,810
    Post Likes
    Originally posted by smokin68
    Manual J tells you the heat loss/gain for an area, and this info can be used to size any heating/cooling system.
    Not so...the potential for downward loss with a radiant floor heating system is great and must be properly analyzed.

    A program design for radiant floor heat is the only program that has this ability...no others will do.


  4. #4
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,610
    Post Likes

    Thumbs up Floor Heat Losses

    Originally posted by simpleman
    [B]
    Originally posted by smokin68
    Manual J tells you the heat loss/gain for an area, and this info can be used to size any heating/cooling system.
    Not so...the potential for downward loss with a radiant floor heating system is great and must be properly analyzed. [B]
    Thermal properties of the composite floor and floor heat loss are addressed adequately in a Manual J load analysis if performed by competent, experienced individuals.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities