01-26-2006, 08:45 AM #1
Manual-J Pros, a question
I have just done a room-by-room Manual J, and observe that one of the bedrooms has disproportionately more heat loss in the winter, compared with the others. Not surprisingly, this bedroom has a tendency to get cold on winter nights.
The room in question is 206 sqft, its summer heat gain at design temperature is 2728 btuh and winter heat loss is 5214. A near-twin room with different exposure is 189 sqft and has summer heat gain 3212 and winter heat loss 4931. Note that one room is "dominant" in winter, it flips to the other in summer.
This is apparently integral to the house design and orientation, so how to live with it is the big question. When the bedroom has adequate airflow for winter needs, it should be excessively cooled in summer. In this climate, winter occurs in short sporadic bursts, so a once-a-year airflow adjustment is not a feasible solution. I cannot think of any comfort solution that does not involve moving parts (or spending a fortune in new windows).
When designing HVAC to make the house comfortable summer and winter, how would a pro try to make the best of this situation?
Thanks for your wisdom -- Pstu, formerly known as P.Student
[Edited by pstu on 01-26-2006 at 08:48 AM]
-
01-26-2006, 01:20 PM #2
Regular Guest
- Join Date
- Mar 2004
- Posts
- 1,042
No moving parts? That's no fun

Looks like a good application for Arzel, to me. You could just have a damper and thermostat in each of those two rooms (not a central zone control) just to prevent overheating/overcooling.
-
01-26-2006, 01:35 PM #3
Professional Member
- Join Date
- Nov 2004
- Posts
- 2,923
Re: Manual-J Pros, a question
I didnt recognise you with that fake moustache,POriginally posted by pstu
When designing HVAC to make the house comfortable summer and winter, how would a pro try to make the best of this situation?
dsign for cooling and add electreic baseboard
-
01-27-2006, 06:02 AM #4
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,263
Re: Manual-J Pros, a question
Set A/C to summer conditions & use a heat blanketOriginally posted by pstu
room-by-room Manual J,
and observe that one of the bedrooms has disproportionately more heat loss in the winter, compared with the others.
The room in question is
206 sqft, its summer heat gain at design temperature is 2728 btuh and winter heat loss is 5214.
A near-twin room with different exposure is
189 sqft and has summer heat gain 3212
............ and winter heat loss 4931.
, so how to live with it is the big question.
When designing HVAC to make the house comfortable summer and winter, how would a pro try to make the best of this situation?
[Edited by pstu on 01-26-2006 at 08:48 AM]
or small (1 kW) heater to maintain bedroom >66ªF
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
01-27-2006, 06:54 AM #5
Professional Member
- Join Date
- Jul 2005
- Posts
- 639
Manual damper in supply. You can get fancy and istall a powered damper with controls and stuff but IMO it's more $$ and headache than it's worth.