Results 14 to 23 of 23
    Oct 2011
    hayward ca
    after the factory charge, and you are still low because of line set, add more till it sweats.
    Quote Originally Posted by Ansonf View Post
    This is NOT a good charging metric.
    With a 50 degree ambient, the dewpoint will be quite low.
    It may not be possible to get the suction line to sweat.
    New Jersey
    How does that compensate for lineset length?
    With that as an unknown, you cannot simply weigh in and go.
    is there not a formula that calculates extra refrigerant for additional liquid line
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
    I'm learning all the time, the tombstone will be my diploma!!!
    Did you ever stop to think, and forget to start again?
    Quote Originally Posted by Tommy1010 View Post
    Indeed, there is.
    Of course, this ASSUMES that you can access the lineset to measure it.
    Aug 2008
    And if you cannot measure the lineset to calculate the required charge, how do you charge it?
    "Touche`" you got me! my "DUH"
    Philadelphia
    Angry
    Wow, Poor customers ...
    Philadelphia
    Oh it will sweat , When the ice starts forming on it because you have 0 degree superheat and a 28 degree suction line slugging liquid into the compressor
    Oct 2007
    Southern Indiana
    Most commercial units don't come with a factory charge weight stamped on them.
    If your running the unit at 50 degrees it should have some type of low ambient kit or a fan cycling switch, just charge to proper superheat and subcooling.
    Oct 2011
    hayward ca
    or you can build an enclosure around your condensor keep it kosey. insulate line set real good. O r have the owner do that.
    Oct 2011
    hayward ca
    Being i n bay area Ca, I ve not had to deal with 50 degree daytime weather.