    Have a Trane RTAA 270 (1997) model, controller is the old adaptive control blue screen with four square buttons, up/down/st.pt down and st.pt up. Comp's A & B running fine, but comp C tries to start, then fails immediately on phase loss. The start contactor not even pulling in. Have checked all phases, resistance through contactors, all o.k. C.T's resistances o.k. The oil pressure switch is made. 115v comes from module board on start up, but that's all. Fails immediately on start-up. Anyone have any ideas? Thanks.
    MEXICO
    check the starter auxiliary contacts they give the boot confirmation falsify interpreted as a phase loss
    The Hot South
    Does this chiller have a y-delta starter? If so, check the auxiliary contacts on the contractors.
    Hey Servicetrane,
    Thanks for the tip. Was looking at the contactors, but not really at the auxillaries. Checked them out and sure enough, welded aux. Thanks for your help. Sorry about the late reply. Cheers.
    Dec 2011
    dubai
    i have rtaa trane chiller and the compressor is part winding and it is fail imidetly even checked for compressor winding,contactor,curent ct all are o.k so waht could be the fault
    The Hot South
    Mustafaali,
    You should start a new thread and you'll get more responses. You also need to give more info. You can't just say "compressor fail, what could it be?". Were not there looking at it. Post exactly what it's doing, what alarms it's calling out, how long it runs, does breaker trip, etc.
    Sep 2010
    miami,fl.
    put on a hard start kit
    Quote Originally Posted by anthonyac1 View Post
    i would like to see how big that kit would be!
    ottawa canada
    Its three phase remember , you will need three hard start kits , dont cross the phases on the hard start kits !!!!!!
    The Hot South
    Quote Originally Posted by graham View Post
    I heard Trane is coming out with a 3 phase hard start kit specifically for the RTAA!
    wait a minute Igan, you said crossing the streams was bad! - Ghostbusters
    Dec 2011
    dubai
    Quote Originally Posted by R123 View Post
    Mustafaali,
    R123
    i checked the winding by meggar test and found its ground and i have anther compressor runing Amps 20 and making noisy
    The Hot South
    What is your meggar reading? Did it blow the fuses or trip the breaker? Did you check the terminal plate?