    frequency drive

    im working on a frequency drive made by teco pa7300 380-460v motor is 15 hp. my sistuation is that they test the fire alarm motor starts to ramp up good. The exhaust fan extracts all the smoke no problem once they reset the smoke alarm at the pannel and the motor starts to ramps down and a fault code pops up fault over voltage. and it will pop up like 3 consecutive times then lock out on fault over voltage. i just downloaded the manual tonight and will head back tomorrow. i have a feeling i might have to change some parammeters. has anybody alse came across this issue?????? Any advice is highly appreciated!!!

  2. #2
    Join Date
    Oct 2009
    Location
    Nova Scotia, Canada
    Posts
    175
    Post Likes
    Sounds like the Decelleration time is too short. I am an ABB factory trained tech and thats usually the case with them
    Follow me @blankscole

  3. #3
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    I agree, what's your deceleration time?

  4. #4
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    2,253
    Post Likes
    Thread Starter
    Quote Originally Posted by CE-TECH View Post
    Sounds like the Decelleration time is too short. I am an ABB factory trained tech and thats usually the case with them
    decelleration time 1 was set to 10.0 seconds and decell time 2 was set for 90 seconds. i lowered the decell time #2 to 20 seconds and it still gives the fault. i wanted to change a few other parameters but the engineer said he only got the approval for 2 false smoke alarm test for the day. need to return tomorrow wednesday 10/26 and try it again. I appreciate all your help and inputs thanks alot!

  5. #5
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    You need to INCREASE your deceleration time, not decrease it. Set your deceleration time #2 back to 90 seconds and INCREASE your deceleration time #1 up to something like 30 or 60 seconds.

    10 seconds is too short for a fan because the inertia in the fan takes longer than 10 seconds to wind down. This turns the motor into a generator and back feeds voltage into the drive which causes the DC bus overvoltage.

  6. #6
    Join Date
    Oct 2009
    Location
    Nova Scotia, Canada
    Posts
    175
    Post Likes
    R123 is correct. Generally an ABB VFD has a default Deceleration time of 30sec. Depending on the size of the blower wheel I have gone as far as 60 sec.
    Follow me @blankscole

  7. #7
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    2,253
    Post Likes
    Thread Starter
    i really appreciate your help ce-tech, and R123. ima go back sometime this week and increase the decell time. I was understanding it backwards. but from your point of view it makes more sense. ill keep you two posted!! Thanks.

  8. #8
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    2,617
    Post Likes
    As said above raise the deceleration to minimum of 60 secs or change stop from ramp to coast if all the motor is for smoke purge.

  9. #9
    Join Date
    Oct 2011
    Location
    MASON NECK VA
    Posts
    17
    Post Likes

    drive problem

    have you megged the motor windings yet. Had the same problem and the decel time was adjusted made no diffrence. The motor was causing a odd back EMF the drive did not like and would lock out over current. MEG the motor to see the diffrence in the windings. Changed the motor problem went away.

  10. #10
    Join Date
    Dec 2003
    Location
    45th Parallel
    Posts
    1,036
    Post Likes
    Set it up for coast to stop like 69 said.
    “If your work speaks for itself, don't interrupt.” ~Henry J. Kaiser

    "Highly efficient equipment and LEED Bldgs are very expensive to maintain in order to keep that efficiency!" ~ Me

  11. #11
    Join Date
    Oct 2011
    Location
    hayward ca
    Posts
    57
    Post Likes
    ill put this threade in my brain for future referance

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •