    I have this Room in my Farm


    Long 9m X Width 6m X High 3 = 162

    One s meter =300 X 162 = 48600 BTU

    48600 BTU / 12000 BTU = 4.05 Ton

    This formula for A/C cooling

    Do you think this formula its give good condition ?

    thanks for

  2. #2
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,857
    Please click on this tab at the top of the page to size the for the heat gain of your house, the only true way to do it.

    Karst means cave. So, I search for caves.

  3. #3
    Join Date
    Jul 2000
    Location
    Louisiana , USA
    Posts
    3,280
    Originally posted by welhan
    I have this Room in my Farm


    Long 9m X Width 6m X High 3 = 162

    One s meter =300 X 162 = 48600 BTU

    48600 BTU / 12000 BTU = 4.05 Ton

    This formula for A/C cooling

    Do you think this formula its give good condition ?

    thanks for
    This is Turtle.

    Hummmmmmm, i have a camp on the lake near here and it is about the same size as your stating about your building and it has a 22,000 btu window unit in it and it does fine at out door temperature of well over 100 degree f.

    Your calulator says i should use 48,000 [4 ton] and i'm doing fine on 22,000 btus [ 1.83 tons] , hummmmmmm, there seem to be a error here somewhere.

    Welhan , i have been down this road 40 years and have never found any straight out formula that would do as a cooling load calculator and work good as to keeping the right temp. in the house.

    You really need to get you a HVAC Manual J calculator and run it on your house. this is the only true guage as to getting the BTU's you need.

    If you wanted to talk about it e-mail me. turtle4airea2bellsouth.net , you know change the 2 to what it should be.

    TURTLE



    [Edited by Mod2 on 01-22-2006 at 10:26 AM]

  4. #4
    Join Date
    Aug 2005
    Posts
    25

    Smile

    THANKS FOR HELP ME MR.turtle

  5. #5
    Join Date
    May 2004
    Posts
    3

    Formula

    Welhan, you might have a good "ballpark" sizing number if you took the 3m height out of your calculation. The "300" number is purely subjective, as some contractors "learn" what they can use for a given "local" design condition. don't oversize the unit. As stated, a Manual J calc is always best.

    Jed

  6. #6
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,548
    You really don't want to put 4 tons of air into a 550 sq ft room unless it is a screen room with open roof. Do the homeowners calculation at the top of this site, it will pay for itself not needing 4 tons of air.
    If everything was always done "by the book"....the book would never change.

  7. #7
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    674
    Look at this guys past posts before giving any sizing advice. He lives in Saudi Arabia and has a summertime high temp of 140F. I don't think any of our good intention guesses will be close. He definitly needs to do a Man J.
    I am the "Wally". All others are meer imitations of the original.

  8. #8
    Good point!

  9. #9
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,271

    Thumbs down What's next ?

    Originally posted by welhan
    I have this Room in my Farm

    Long 9m X Width 6m X High 3 = 162
    One s meter =300 X 162 = 48600 BTU

    48600 BTU / 12000 BTU = 4.05 Ton

    Do you think this formula its give good condition ?
    No but it's in the ball park.
    You need somewhere between 0.5 - 10 tons
    Depending on whether you keep the windows open or not.


    L O L
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  10. #10
    Join Date
    Aug 2005
    Posts
    25

    Smile thankssssssssssssssssss

    It’s my mistake to Wright here I thought get help but my behavior STOP me to say bad things any way thanks for good to people always helping this is last time to visit this web page.

    welhan

  11. #11
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    674
    Don't get offended because of what I said because it wasn't meant that way. I only wanted to point out to everyone that you live in a different enviroment than we, in USA, do. Other than the guys that live in the desert southwest, most of us don't have experience, on a day to day basis, with the extream heat that you have. I'm in Michigan and a room that size, 486 sq ft, would not even need a ton of cooling. My initial response to your post would be that 4 ton is way too much and I think the rest of us would respond the same.
    So you see that it's not that we don't want to advise, but we really can't based on our experience without doing a heat gain on the structure.