    2 condensers, one evaporator

    Can I replace a 10 ton single circuit, AC only condensing unit with two 5 ton split systems condensers?
    I have a situation where I cant replace the existing R-22 evaporator and a R22 condensing unit is not available.
    I plan on running the units in tandem. What controls should I have to make this work? How can I ensure proper and equal oil return? The old unit is 230V 3phase, 5/8 LL and 1 3/8 suction line.
    Any input would help.

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    35,731
    Post Likes
    I wouldn't. Get a matched 2 circuit coil. Otherwise, may have to use solenoids or checkvalves to aim refrigerant the right direction.

  3. #3
    Join Date
    Jul 2001
    Location
    maryland
    Posts
    1,363
    Post Likes
    Buy a Goodman 10ton R-22 condenser.
    Saving the world...one service call at a time.

  4. #4
    Join Date
    Sep 2008
    Location
    Mesquite Tx.
    Posts
    390
    Post Likes
    One of the compressors will end up with all the oil. Then you know what happens to the other one.
    Nos operor non pensio volutabrum

  5. #5
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    480
    Post Likes
    the dual-circuit evaporator?

  6. #6
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,860
    Post Likes
    you can replace it with 2- 5 ton systems twinned into the same duct.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  7. #7
    Join Date
    Oct 2011
    Location
    Baltimore
    Posts
    4
    Post Likes
    Checked with Goodman he in MD. No 10 ton R22 units available. The evaporator I have is a 3 circuit horizontal coil in a section of duct being used for a process. Changing that coil is not an option at this time. I'm thinking if I split the piping even between the two units, put check valves in the liquid lines, and install crankcase heaters, this might work. If only I could install a oil equalization linebetween the compressors.... Thoughts?

  8. #8
    Join Date
    Apr 2007
    Location
    Kaufman county, Texas
    Posts
    11,364
    Post Likes
    I am having a hard time believing you cannot get a 10 ton condenser, might need to make some more calls.

    If you really cannot, can you repair the old one in any way? What is wrong with it?
    "You boys are really making this thing harder than it has to be". Me

    "I am not here to rescue you, I am bringing you along for emergency rations" Quark.

    Service calls submitted after 3PM will be posted the next business day.

    I give free estimates [Wild Ass Guesses] over the phone.

    My front door is locked. For your personal protection.

  9. #9
    Join Date
    Jul 2001
    Location
    maryland
    Posts
    1,363
    Post Likes
    Quote Originally Posted by FitterTom View Post
    Checked with Goodman he in MD. No 10 ton R22 units available. The evaporator I have is a 3 circuit horizontal coil in a section of duct being used for a process. Changing that coil is not an option at this time. I'm thinking if I split the piping even between the two units, put check valves in the liquid lines, and install crankcase heaters, this might work. If only I could install a oil equalization linebetween the compressors.... Thoughts?
    I JUST BOUGHT ONE about three weeks ago.

    Call the Capitol Heights branch.
    Saving the world...one service call at a time.

  10. #10
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    480
    Post Likes
    which is the current model or brand of your machine?

  11. #11
    Join Date
    Dec 2005
    Posts
    1,953
    Post Likes
    Quote Originally Posted by FitterTom View Post
    Checked with Goodman he in MD. No 10 ton R22 units available. The evaporator I have is a 3 circuit horizontal coil in a section of duct being used for a process. Changing that coil is not an option at this time. I'm thinking if I split the piping even between the two units, put check valves in the liquid lines, and install crankcase heaters, this might work. If only I could install a oil equalization linebetween the compressors.... Thoughts?
    Please don't do it. Please don't try it. You will give HVAC a bad name.

    Customer WILL HAVE to spend the money. Else, back off.

  12. #12
    Join Date
    Oct 2011
    Location
    Baltimore
    Posts
    4
    Post Likes
    Wow. Goodman in Frederick has a 10 ton condensing unit. I checked a few weeks ago and none were available. Problem solved, thanks.