    Carrier 30RBA160 not staging up

    Hi, need some help here, since Carrier has washed their hands of this problem, I have a 30RB160, 2005, I need to change 1 compressor [again] and need to disable the "A" circuit to work on it, when I do this, "B" circuit will not stage up and maintain water temp, only 1 "B" compressor comes on with Hot Gas, and just runs forever, no other compressor{B circuit} will stage up, I've done this in the past and never had a problem with "B" cuircuit staging up and controling water temp. I've tried to stage on Circuit "A" just to see if I can do that, and it works perfectly. Carrier has asked me to do several things to it and still doesn't work, [so many, I can't name them here] I've had to replace so much on this machine, I wish I could trade it for something else. The last response I got from Carrier was,"We don't know why it's doing this, Sorry" Any help would be greatly appreciated. Lonnie

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Are there any override modes on preventing it from loading up? Has any software been upgraded? Power problems ? Why are your compressors failing , contagious welded?

  3. #3
    Join Date
    Aug 2002
    Location
    Greenville SC
    Posts
    443
    Post Likes
    I had one do this and I downloaded a new program into it. Solved the problem, at least on this occasion.

  4. #4
    Join Date
    Aug 2002
    Location
    Greenville SC
    Posts
    443
    Post Likes
    The chiller will also run much better with the latest and greatest progam.

  5. #5
    Join Date
    Oct 2011
    Posts
    43
    Post Likes
    Thread Starter
    Thanks for the replies. No override modes. Don't know reason for failures, but thinking ,like was suggested, need upgraded version and maybe will solve problems, not all the same problem with compressors, 3 were vibrating so bad, it broke the discharge line twice, 2 were shorted, the rest just locked up. Will see if Carrier wan't to talk to me to upgrade my software. Thanks. Lonnie

  6. #6
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by 2wings View Post
    Thanks for the replies. No override modes. Don't know reason for failures, but thinking ,like was suggested, need upgraded version and maybe will solve problems, not all the same problem with compressors, 3 were vibrating so bad, it broke the discharge line twice, 2 were shorted, the rest just locked up. Will see if Carrier wan't to talk to me to upgrade my software. Thanks. Lonnie
    What be the serial number on this machine?

  7. #7
    Join Date
    Oct 2011
    Posts
    43
    Post Likes
    Thread Starter
    Serial Number=4005Q80419

  8. #8
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by 2wings View Post
    Serial Number=4005Q80419
    What does your phase monitor look like?

  9. #9
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by 2wings View Post
    Serial Number=4005Q80419
    What does your phase monitor look like?

  10. #10
    Join Date
    Oct 2011
    Posts
    43
    Post Likes
    Thread Starter
    No phase monitor.

  11. #11
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by 2wings View Post
    No phase monitor.
    Unless someone took it out it's in there somewhere if not I think we found your problem.

  12. #12
    Join Date
    Oct 2011
    Posts
    43
    Post Likes
    Thread Starter
    Unless it's built into one of the circuit boards, I don't see it, this was low bid, so if they could leave something out, they might have done that. I'll look again. Lonnie

  13. #13
    Join Date
    Aug 2002
    Location
    Greenville SC
    Posts
    443
    Post Likes
    It's in there. All the RB's have one.

  14. #14
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by 2wings View Post
    Unless it's built into one of the circuit boards, I don't see it, this was low bid, so if they could leave something out, they might have done that. I'll look again. Lonnie
    Put your email address in your profile please. I think we need to talk further about this.

  15. #15
    Join Date
    Oct 2011
    Posts
    43
    Post Likes
    Thread Starter
    OK, I think I found my problem, first off, I found the phase monitor, it's NOT a Siemens, it's a circuit board about 3" square. Second, since I wasn't getting any help from Carrier, I thought I'd start looking in the scrolling marque to see if I could come up with something, after about an hour or so, I found it, I was in the "Temp" category and was in Circuit B and went to "Superheat" ,now remeber, circuit B is not running, and the superheat was 189*, I thought this was a little high my suction gas thermister was out of calibration, it wasn't open or shorted, just out of calibration, I've had the alarm light on before when it was open or shorted, so I replaced the thermister and it runs great. I am going to send my board in and get it updated to the latest version. I want to thank all who gave me ideas and things to try.

  16. #16
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by thegoodlistener View Post
    Are there any override modes on preventing it from loading up? Has any software been upgraded? Power problems ? Why are your compressors failing , contagious welded?
    Just rembember override modes are your friend. I figured this might be your problem.

  17. #17
    Join Date
    Oct 2011
    Posts
    43
    Post Likes
    Thread Starter
    Quote Originally Posted by thegoodlistener View Post
    Just rembember override modes are your friend. I figured this might be your problem.
    Maybe you could explain to me just what a override mode is, I'm not clear on this since I didn't see any override modes,

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •