OK, I think I found my problem, first off, I found the phase monitor, it's NOT a Siemens, it's a circuit board about 3" square. Second, since I wasn't getting any help from Carrier, I thought I'd start looking in the scrolling marque to see if I could come up with something, after about an hour or so, I found it, I was in the "Temp" category and was in Circuit B and went to "Superheat" ,now remeber, circuit B is not running, and the superheat was 189*, I thought this was a little high
my suction gas thermister was out of calibration, it wasn't open or shorted, just out of calibration, I've had the alarm light on before when it was open or shorted, so I replaced the thermister and it runs great. I am going to send my board in and get it updated to the latest version. I want to thank all who gave me ideas and things to try.
-