Results 1 to 3 of 3
  1. #1
    Join Date
    Jul 2011
    Location
    Alabama
    Posts
    5

    Confused Trane RTAC and CGAM chillers

    Does anyone know if Trane CGAM or RTAC model air cooled chillers can be retrofitted with ice making equipment for a thermal storage application? Have several of these chillers that were not purchased with the ice making option and we are now considering thermal storage. Is there a retrofit kit? Part #? Is it hardware and software?

  2. #2
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,433
    yes, there is no kit . the ch530 holds all setpoints for ice build mode. don't forget glycol
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  3. #3
    Join Date
    Mar 2007
    Location
    Home of the newly wed and the nearly dead
    Posts
    2,947
    Both of those chillers will accept a contact closure ice making input, or you can put them into ice mode with software using BacNet, Lon, or Tracer. Just don't expect your 10 degree, 200 ton machine to still be a 10 degree, 200 ton machine when you start pumping a >25% glycol solution through it. You have to make sure your pumps are sized correctly, as well. The pumping requirements and characteristics of glycol are different than plain water.

    In most cases, if the machines are relatively new and you contact the factory, they can run a re-selection on the chiller, which will tell you how your chiller will perform on ice making duty.
    Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.

    "It's called the american dream because you have to be asleep to believe it" -George Carlin

    "A nation of sheep begets a government of wolves" -Edward R. Murrow

    "I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney

    Buy american made goods & support locally owned businesses!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •