    I FOUND THE CIRCUIT WIRING DIAGRAM WHITCH IS STICKED ON THE BACK OF THE FRONT PANAL IS WRONG. ON THE DIAGRAM,THERE IS A WIRE CONNECTED BETWEEN CM/T7 AND TC/COM WHITCH WOULD SHORT HPS AND LPS.THIS WIRE ACTUALLY GOES FROM CM/T7 TO TC1/COM, THERE IS NO DIRECT CONNECTION BETWEEN CM/T7 AND HOT LINE. THIS TERMINAL CALLED TC/COM DOES NOT EXIST AT ALL,AND THE CONNECTION BETWEEN TC1/COM AND HOT LINE DOES NOT EXIST EITHER.

  2. #2
    Join Date
    Jul 2005
    Posts
    947
    Please stop with the yelling already... :-(

  3. #3
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,132

    Please quit yelling...

    Perhaps you should have read the instructions before calling.

  4. #4
    Join Date
    Nov 2004
    Posts
    240
    Relax nisong ... If there is a T10 and T11 and your CM, then it has been replaced and the new one is wired different from the original. There was a problem with the bypass relays on the original ones.

  5. #5
    Join Date
    Dec 2005
    Posts
    12
    It does not have T11 and T10, so it must be original.Since it was installed,this unit rans for a few days then stop by itself,has to be reset to start.Replaced all controls except bypass relay,it remaines the same.

    [Edited by nisong on 01-20-2006 at 11:37 PM]

  6. #6
    Join Date
    May 2005
    Location
    Calgary, Alberta, Canada
    Posts
    92
    OMG who is paying the bill on this?
    Yes we have air conditioning in our igloos.

  7. #7
    Join Date
    Nov 2005
    Location
    Chicago
    Posts
    34

    30GT

    NISONG

    If this unit has a FloTronic computer driving, the random stopping doesn’t surprise me.
    We have a 30GT080 that has a mind of it’s own on occasion.
    The last time we had a problem the computer data said the unit was running but no compressors where running. I changed the two contactors on the 40-ton compressor and have not had this problem lately. This computer is quit sensitive to RFI per Carrier.

    cvw

    [Edited by cvw on 01-24-2006 at 07:29 AM]

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event