Page 1 of 2 12 LastLast
Results 1 to 13 of 17
  1. #1
    Join Date
    Jul 2005
    Location
    Wilmington,De
    Posts
    10
    Post Likes
    can someone explain the operation of a wye-delta closed transition starter? What is the function of the "shorting" contactor; and what are the resistors used for? Thanks in advance!

  2. #2
    Join Date
    Jan 2001
    Location
    Nebraska
    Posts
    319
    Post Likes
    phillyg:

    Try this web site it will explian it better than I could.

    http://www.lmphotonics.com/star_delta.htm

  3. #3
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,588
    Post Likes
    you will need a diagram and a sequence of what is going on. the shorting of the contactor is actually reconfiguring the motor windings. I could not explain it here. try to find someone to go over it with you with the diagrams.

  4. #4
    Join Date
    Aug 2003
    Posts
    1,311
    Post Likes
    Now i thought that primary resistance starting and a wye-delta starter were two different animals.

  5. #5
    mancuso jr is offline Professional Member t-bad email address, Contact Admin
    Join Date
    Aug 2005
    Posts
    31
    Post Likes
    No Primary Res. Starters are different in that they use Res. moment to limit inrush then close another contact for full voltage , you could say they are more related to auto transformer starters than y-delta.

  6. #6
    Join Date
    Aug 2000
    Location
    Under my tree
    Posts
    5,087
    Post Likes
    Due you work with J. Fusco?
    Originally posted by mancuso jr
    No Primary Res. Starters are different in that they use Res. moment to limit inrush then close another contact for full voltage , you could say they are more related to auto transformer starters than y-delta.
    To much work with too little time!!!!

  7. #7
    Join Date
    Jan 2005
    Posts
    605
    Post Likes
    The resistor bank on a closed transition Y Delta starter, actually carries the load during the "closed transition". This will produce less arcing as the the contactors make and break. They are in the circuit for less than 1/10 th of a second. If this takes longer, the incomplete transition fuse blows ( or brakes depending on your terminology ), somewhere in the 1/10 of an amp. fuse.

    [Edited by r718 on 01-20-2006 at 08:56 PM]

  8. #8
    Join Date
    Jul 2005
    Location
    Wilmington,De
    Posts
    10
    Post Likes
    Thread Starter
    No Abs, I don't know J. Fusco

  9. #9
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    we installed 4 120 ton york air cooled screws. when units would start up they would go off. we found the cover plate of some of the starters that cover the control voltage connection had fallen off inside the starters preventing them from switching. i thing they would go off on high start amps. but just giving yall a heads up.

  10. #10
    Join Date
    Jan 2001
    Location
    Nebraska
    Posts
    319
    Post Likes
    Hey Guys:

    I retired 10 years ago this month so I am out the loop on what is current.

    Are they still shipping new stuff with wye/delta?

    I would have thought that by now solid state starting technology would have pretty much replaced most of the other reduced voltage starting methods.

    Thanks for any input. Tom

  11. #11
    Join Date
    Oct 2005
    Location
    USA
    Posts
    8
    Post Likes
    1

  12. #12
    Join Date
    Oct 2005
    Location
    USA
    Posts
    8
    Post Likes
    2

  13. #13
    Join Date
    Oct 2005
    Location
    USA
    Posts
    8
    Post Likes
    3

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.