can someone explain the operation of a wye-delta closed transition starter? What is the function of the "shorting" contactor; and what are the resistors used for? Thanks in advance!
-
01-19-2006, 06:50 PM #2
Professional Member
- Join Date
- Jan 2001
- Location
- Nebraska
- Posts
- 319
phillyg:
Try this web site it will explian it better than I could.
http://www.lmphotonics.com/star_delta.htm
-
01-19-2006, 07:33 PM #3
you will need a diagram and a sequence of what is going on. the shorting of the contactor is actually reconfiguring the motor windings. I could not explain it here. try to find someone to go over it with you with the diagrams.
-
01-19-2006, 08:36 PM #4
Regular Guest
- Join Date
- Aug 2003
- Posts
- 1,311
Now i thought that primary resistance starting and a wye-delta starter were two different animals.
-
01-20-2006, 06:06 AM #5
Professional Member t-bad email address, Contact Admin
- Join Date
- Aug 2005
- Posts
- 31
No Primary Res. Starters are different in that they use Res. moment to limit inrush then close another contact for full voltage , you could say they are more related to auto transformer starters than y-delta.
-
01-20-2006, 07:51 PM #6
Professional Member
- Join Date
- Aug 2000
- Location
- USA
- Posts
- 4,935
Due you work with J. Fusco?
Originally posted by mancuso jr
No Primary Res. Starters are different in that they use Res. moment to limit inrush then close another contact for full voltage , you could say they are more related to auto transformer starters than y-delta.Your poor planning does not constitute an emergency on my part!!!!
-
01-20-2006, 08:54 PM #7
Professional Member
- Join Date
- Jan 2005
- Posts
- 587
The resistor bank on a closed transition Y Delta starter, actually carries the load during the "closed transition". This will produce less arcing as the the contactors make and break. They are in the circuit for less than 1/10 th of a second. If this takes longer, the incomplete transition fuse blows ( or brakes depending on your terminology ), somewhere in the 1/10 of an amp. fuse.
[Edited by r718 on 01-20-2006 at 08:56 PM]
-
01-21-2006, 09:09 AM #8
Regular Guest
- Join Date
- Jul 2005
- Posts
- 10
No Abs, I don't know J. Fusco
-
01-21-2006, 11:32 AM #9
Member
- Join Date
- Mar 2003
- Posts
- 1,877
we installed 4 120 ton york air cooled screws. when units would start up they would go off. we found the cover plate of some of the starters that cover the control voltage connection had fallen off inside the starters preventing them from switching. i thing they would go off on high start amps. but just giving yall a heads up.
-
01-21-2006, 01:59 PM #10
Professional Member
- Join Date
- Jan 2001
- Location
- Nebraska
- Posts
- 319
Hey Guys:
I retired 10 years ago this month so I am out the loop on what is current.
Are they still shipping new stuff with wye/delta?
I would have thought that by now solid state starting technology would have pretty much replaced most of the other reduced voltage starting methods.
Thanks for any input. Tom
-
01-21-2006, 09:39 PM #11
Professional Member
- Join Date
- Oct 2005
- Location
- USA
- Posts
- 8
1
-
01-21-2006, 09:39 PM #12
Professional Member
- Join Date
- Oct 2005
- Location
- USA
- Posts
- 8
2
-
01-21-2006, 09:40 PM #13
Professional Member
- Join Date
- Oct 2005
- Location
- USA
- Posts
- 8
3


Reply With Quote