    Trane GEVB Water Source Heat Pump Won't Cool

    I live in a high rise condo and my unit has a Trane GEVB04811R commercial water source heat pump. Starting a couple days ago I'd set the thermostat to cooling to 73F but the actual temperature never goes below 77F, with the Trane running on the whole time. I tried putting in a new filter and then flipping the breaker with no improvement. I then removed the top and bottom front panels and nothing looked out of the ordinary.

    What else should I look into or try? Thanks for your input in advance.

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    3,371
    you most likely have a water flow restriction (a plugged up strainer). this will require the unit to be shut down, water section isolated and the strainer removed and cleaned.

    i would strongly recommend having a professional perform this service. the water side may have glycol (an antifreeze) in the water loop. this chemical is expensive to replace if you lose too much and can really make a mess.

    it should only take about 1 day or less to perform this service if you have isolation valves. if not, it could take days depending on how much of the system needs to be drained.
    The weak aren't destroyed by the strong.
    The weak are destroyed by the under-estimated.

  3. #3
    Thank you very much, Jay

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,892
    This is the Ask Our Pro's forum. In order to post advice here, you must have verified qualifications and have been approved by the AOP Committee.

    You can find the rules for posting and qualifications here.
    Last edited by jpsmith1cm; 11-05-2011 at 11:51 AM. Reason: Removed quote

  5. #5
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,506
    Here I will validate your suggestion.

    Waterflow *
    Last edited by jpsmith1cm; 11-05-2011 at 11:52 AM. Reason: removed non-AOP quote
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,892
    Not a problem, james32

    I'm just trying to keep the peace in the AOP forums.

    Also, keep in mind that you still need your * to post in the AOP.

    Also, I'm not trying to invalidate or degrade anyones advice.
    Last edited by jpsmith1cm; 11-05-2011 at 11:53 AM.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •