    1 Damper 2 Furnaces?

    My boss ask if two furnaces can control one damper independantly. I have not seen the job but was told there is one fresh air inlet that is piped into two seperate furnaces via the return duct. This air damper is to open, only when at least one of the two furnaces are running, does not matter which, and to be open when both are running. The furnaces are not twined, each have a seperate T-Stat and control different rooms. How can I control this damper with two furnaces, but not to back-feed to the furnace that is off?

    Thanks, Keith


    I'm an HVAC/R service Tech! Just have not got enough post to be pro yet.

  2. #2
    Join Date
    Jan 2011
    Location
    greenville , sc
    Posts
    716
    Post Likes
    ive never seen it done that way Keith , but hey i have never piloted a plane either........

    im interested in knowing WHY this is done in the first place?

    seems to me that something isn't kosher.
    why would one expect two separate furnaces to share a duct system , especially if they aren't twinned?

    keep us posted.
    catch a man a fish , feed him for a day.
    teach a man to fish , ruin a good business opportunity.

  3. #3
    Join Date
    Oct 2007
    Location
    Southern Indiana
    Posts
    123
    Post Likes
    Relay!

  4. #4
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,257
    Post Likes
    Use a 24v open, spring return damper actuator.

    Use a current switch on the blower common wire for each furnace and wire the switches in parallel using 24 volts from somewhere. Just make sure the transformer has enough va to stroke the damper actuator..

    When one of the two blowers, or both are on, it closes the current switch(s) and commands the damper to open..

    nice and easy.

    Im sure more people will chime in with different solutions, theres more than one way to skin a cat.

  5. #5
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    power the OA motor drive direct then add one relay per boiler 24V coil N.O. contacts in stacked series with the hot wire motor voltage either or will drive it on a heating call..if the boilers are commercial size you might have dry N.O. contacts within the control panel there
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  6. #6
    Join Date
    Mar 2004
    Location
    Panama City, FL
    Posts
    28
    Post Likes
    Thread Starter

    Confused

    I could use two current sensing relays on the G wire of each furnace. When ever the sensor picks up current the relay would close and power the damper. This would allow for a seperate transformer to power the damper correct? I know there are avalible items from electronic suppliers, but has anyone seen one at the HVAC supplier? Would one of these sensor pick up the slight current going through the G wire?

    Thanks again.

    Would something like this work?
    http://www.johnstonesupply.com/store...odb12-020.html

  7. #7
    Join Date
    Jan 2011
    Location
    greenville , sc
    Posts
    716
    Post Likes
    i still would like to know why this set-up is being used?
    catch a man a fish , feed him for a day.
    teach a man to fish , ruin a good business opportunity.

  8. #8
    Join Date
    Mar 2010
    Location
    Hot Desert SW
    Posts
    27
    Post Likes
    (2) relays, (1) actuator- preferably powered from a seperate power source than the furnaces. Relay coils enegized from G to C on each furnace, parallel n.o. contacts to actuator. Done

  9. #9
    Join Date
    Oct 2011
    Location
    North Phoenix
    Posts
    37
    Post Likes
    Quote Originally Posted by jeremyhall.tech.sc View Post
    i still would like to know why this set-up is being used?
    It is only for fresh air make up if I read the OP correctly. We don't the the age of the building, but this could have been installed to bring the building up to code (%) of make up air.

    Could have only been enough room for (X) size make up air, so 1 duct 2 units, this is not at all uncommon in older buildings.

    Reasons can be endless, that one just makes the most sense to me.

  10. #10
    Join Date
    Oct 2011
    Location
    Las Vegas, NV
    Posts
    656
    Post Likes
    I've only seen two furnaces on the same duct system if they were twinned. If they aren't twinned, wouldn't there need to be some sort of barometric damper, just in case only one of the furnaces are running? If only one was running, couldn't the supply air blow backwards through the furnace that isn't running? I could be wrong, but I could imagine that type of scenario happening, if there wasn't a damper to stop the air from going back through the furnace that's off.

  11. #11
    Join Date
    Mar 2004
    Location
    Panama City, FL
    Posts
    28
    Post Likes
    Thread Starter
    Quote Originally Posted by *TEEKAY* View Post
    (2) relays, (1) actuator- preferably powered from a seperate power source than the furnaces. Relay coils enegized from G to C on each furnace, parallel n.o. contacts to actuator. Done

    That's it!!! I can't believe I did not think of that, I feel like a dumb

    I was told the damper opens and lets fresh combustion air for each furnace, still have never seen the job.

    Thanks

  12. #12
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,257
    Post Likes
    ....

  13. #13
    Join Date
    Feb 2009
    Location
    Thonotosassa, FL
    Posts
    804
    Post Likes
    Quote Originally Posted by morepower7701 View Post
    That's it!!! I can't believe I did not think of that, I feel like a dumb

    I was told the damper opens and lets fresh combustion air for each furnace, still have never seen the job.

    Thanks
    If you are using it to bring in fresh air when the heat is on you need to wire it in to w-c not g-c it will only open when you have the fan turned on or the ac is on. I would think you need it for heat. thinking it for freash air to the furnace room.
    you could put it on a curnant sensing relay on the blower motor to a relay for the damper.

  14. #14
    Join Date
    Mar 2010
    Location
    Hot Desert SW
    Posts
    27
    Post Likes
    Yep, W and C, I misunderstood the intent of the damper

  15. #15
    Join Date
    Jan 2013
    Posts
    2
    Post Likes
    Can someone draw a diagram of this? and where s a good place to get said relays... link???

  16. #16
    Join Date
    Oct 2006
    Location
    tx
    Posts
    32
    Post Likes
    If the damper is for combustion air.What if the damper fails to open. Don't think dampers are allowed for combustion air by code

  17. #17
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    There is a company that makes the product you need right out of the box.
    The company is called Hoyme.
    The part number is F2. You can get them in 4-8" round duct.
    Very easy to install and prewired.
    Wired in series with W on both furnaces, motor fails open to allow heat if something goes wrong.

    Made in Canada, so it's bullet proof ;-)

  18. #18
    Join Date
    Jan 2013
    Posts
    21
    Post Likes
    Im a bit confused the previous threat of wiring it to the w-c would be correct to have it open for heating. It sounds like you are talking about combustion air and dampers if this is the case this is a life safty issue and you would really have to look at manufacturers suggestions. For makeup air in the boiler it is not unusual to have a tie in to the burner contact point on each boiler to open the dampers.

  19. #19
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Quote Originally Posted by morepower7701 View Post
    My boss ask if two furnaces can control one damper independantly. I have not seen the job but was told there is one fresh air inlet that is piped into two seperate furnaces via the return duct. This air damper is to open, only when at least one of the two furnaces are running, does not matter which, and to be open when both are running. The furnaces are not twined, each have a seperate T-Stat and control different rooms. How can I control this damper with two furnaces, but not to back-feed to the furnace that is off?

    Thanks, Keith


    I'm an HVAC/R service Tech! Just have not got enough post to be pro yet.
    As previously suggested last year when this thread was created (2) current sensing relays in series with actuator. An independent power source would be preferred in this application due to one or the other being shut down for what ever reason.

    For all those that have suggested that it might be a combustion air damper and that you cannot use an actuator with a combustion damper, well you are wrong on both counts.

    The combustion air wither provided from an outside air damper or a combustion air fan must be proven before the pre-purge takes place, during the run cycle and during any post purge cycle.

    CSD-1 and others provide the guide lines here.

  20. #20
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    Post deleted.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •