Yep, W and C, I misunderstood the intent of the damper
-
01-22-2013, 04:41 AM #15
New Guest
- Join Date
- Jan 2013
- Posts
- 2
Can someone draw a diagram of this? and where s a good place to get said relays... link???
-
01-22-2013, 09:24 AM #16
Professional Member
- Join Date
- Oct 2006
- Location
- tx
- Posts
- 19
If the damper is for combustion air.What if the damper fails to open. Don't think dampers are allowed for combustion air by code
-
01-22-2013, 09:31 AM #17
There is a company that makes the product you need right out of the box.
The company is called Hoyme.
The part number is F2. You can get them in 4-8" round duct.
Very easy to install and prewired.
Wired in series with W on both furnaces, motor fails open to allow heat if something goes wrong.
Made in Canada, so it's bullet proof ;-)
-
01-22-2013, 11:31 AM #18
Professional Member
- Join Date
- Jan 2013
- Posts
- 19
Im a bit confused the previous threat of wiring it to the w-c would be correct to have it open for heating. It sounds like you are talking about combustion air and dampers if this is the case this is a life safty issue and you would really have to look at manufacturers suggestions. For makeup air in the boiler it is not unusual to have a tie in to the burner contact point on each boiler to open the dampers.
-
01-22-2013, 11:49 AM #19
As previously suggested last year when this thread was created (2) current sensing relays in series with actuator. An independent power source would be preferred in this application due to one or the other being shut down for what ever reason.
For all those that have suggested that it might be a combustion air damper and that you cannot use an actuator with a combustion damper, well you are wrong on both counts.
The combustion air wither provided from an outside air damper or a combustion air fan must be proven before the pre-purge takes place, during the run cycle and during any post purge cycle.
CSD-1 and others provide the guide lines here.
-
01-22-2013, 12:44 PM #20
Post deleted.
"The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
"Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
"Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin
-
01-22-2013, 02:09 PM #21
New Guest
- Join Date
- Jan 2013
- Posts
- 2
I already have a motorized damper I plan to use in the line right after it enters the house. I just need a diagram on how to wire it and where I can get the relays. link preferred.
-
01-23-2013, 09:14 PM #22
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 291
Check out Tjernlund CPC-3.