    1 Damper 2 Furnaces?

    My boss ask if two furnaces can control one damper independantly. I have not seen the job but was told there is one fresh air inlet that is piped into two seperate furnaces via the return duct. This air damper is to open, only when at least one of the two furnaces are running, does not matter which, and to be open when both are running. The furnaces are not twined, each have a seperate T-Stat and control different rooms. How can I control this damper with two furnaces, but not to back-feed to the furnace that is off?

    Thanks, Keith


    I'm an HVAC/R service Tech! Just have not got enough post to be pro yet.

  2. #2
    Join Date
    Jan 2011
    Location
    greenville , sc
    Posts
    718
    ive never seen it done that way Keith , but hey i have never piloted a plane either........

    im interested in knowing WHY this is done in the first place?

    seems to me that something isn't kosher.
    why would one expect two separate furnaces to share a duct system , especially if they aren't twinned?

    keep us posted.
    catch a man a fish , feed him for a day.
    teach a man to fish , ruin a good business opportunity.

  3. #3
    Join Date
    Oct 2007
    Location
    Southern Indiana
    Posts
    94
    Relay!

  4. #4
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,064
    Use a 24v open, spring return damper actuator.

    Use a current switch on the blower common wire for each furnace and wire the switches in parallel using 24 volts from somewhere. Just make sure the transformer has enough va to stroke the damper actuator..

    When one of the two blowers, or both are on, it closes the current switch(s) and commands the damper to open..

    nice and easy.

    Im sure more people will chime in with different solutions, theres more than one way to skin a cat.

  5. #5
    Join Date
    Oct 2001
    Posts
    6,966
    power the OA motor drive direct then add one relay per boiler 24V coil N.O. contacts in stacked series with the hot wire motor voltage either or will drive it on a heating call..if the boilers are commercial size you might have dry N.O. contacts within the control panel there
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  6. #6
    Join Date
    Mar 2004
    Location
    Knoxville, TN
    Posts
    24

    Confused

    I could use two current sensing relays on the G wire of each furnace. When ever the sensor picks up current the relay would close and power the damper. This would allow for a seperate transformer to power the damper correct? I know there are avalible items from electronic suppliers, but has anyone seen one at the HVAC supplier? Would one of these sensor pick up the slight current going through the G wire?

    Thanks again.

    Would something like this work?
    http://www.johnstonesupply.com/store...odb12-020.html

  7. #7
    Join Date
    Jan 2011
    Location
    greenville , sc
    Posts
    718
    i still would like to know why this set-up is being used?
    catch a man a fish , feed him for a day.
    teach a man to fish , ruin a good business opportunity.

  8. #8
    Join Date
    Mar 2010
    Location
    Hot Desert SW
    Posts
    27
    (2) relays, (1) actuator- preferably powered from a seperate power source than the furnaces. Relay coils enegized from G to C on each furnace, parallel n.o. contacts to actuator. Done

  9. #9
    Join Date
    Mar 2004
    Location
    Knoxville, TN
    Posts
    24
    Quote Originally Posted by *TEEKAY* View Post
    (2) relays, (1) actuator- preferably powered from a seperate power source than the furnaces. Relay coils enegized from G to C on each furnace, parallel n.o. contacts to actuator. Done

    That's it!!! I can't believe I did not think of that, I feel like a dumb

    I was told the damper opens and lets fresh combustion air for each furnace, still have never seen the job.

    Thanks

  10. #10
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,064
    ....

  11. #11
    Join Date
    Feb 2009
    Location
    Fox Lake IL
    Posts
    457
    Quote Originally Posted by morepower7701 View Post
    That's it!!! I can't believe I did not think of that, I feel like a dumb

    I was told the damper opens and lets fresh combustion air for each furnace, still have never seen the job.

    Thanks
    If you are using it to bring in fresh air when the heat is on you need to wire it in to w-c not g-c it will only open when you have the fan turned on or the ac is on. I would think you need it for heat. thinking it for freash air to the furnace room.
    you could put it on a curnant sensing relay on the blower motor to a relay for the damper.

  12. #12
    Join Date
    Mar 2010
    Location
    Hot Desert SW
    Posts
    27
    Yep, W and C, I misunderstood the intent of the damper

  13. #13
    Can someone draw a diagram of this? and where s a good place to get said relays... link???

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event