11-08-2011, 04:00 AM #14
Since it's happening to all of them, the main thing they have in common is the power source. I those are all good ideas. You could check the electrical room in the building, the breaker for the panel for the hvac? loose main line contact, difference of how much from there to your units?
-
11-08-2011, 06:53 PM #15
Professional Member
- Join Date
- Jun 2005
- Location
- Henrico,VA
- Posts
- 69
Agreed.I am looking at voltage/power recording options now
A.B.C.-always be careful!
-
11-11-2011, 11:40 AM #16
Found same kinda pblm on McQuay RTU onetime. Eventually learned it only happned during or after rainy weather. Control section was under neg pressure from supply fan and cabinet panels let water draw in and trickle down inside sufficiently to short terminal block on back wall. Of course on a dry day, could not see reason for blown fuses. Made up sheetmetal stand-off for terminal block and later made better panel seals.
-
11-11-2011, 06:30 PM #17
Professional Member
- Join Date
- Jun 2005
- Location
- Henrico,VA
- Posts
- 69
Thats good to know,thanks for sharing.
btw Welcome to the forumsA.B.C.-always be careful!
-
11-11-2011, 11:32 PM #18
Regular Guest
- Join Date
- Nov 2010
- Posts
- 10
i just had the same problem
installed phase monitor- alarm on under/over voltage almost everyday.
i thought that was causing the fuse to blow almost every two days but i finally spent time on tracing all the wires and found that one wire was rubbing to a point were the intermittent blowing fuse was happening. replaced wire and now the a/c been running fine.
-
11-12-2011, 02:20 PM #19
Professional Member*
- Join Date
- Oct 2003
- Location
- las vegas
- Posts
- 1,505
-
11-13-2011, 01:00 PM #20
I f you think about it a blown fuse is usually always motor , or wire short.
-
11-13-2011, 01:35 PM #21
Professional Member*
- Join Date
- Oct 2003
- Location
- las vegas
- Posts
- 1,505
in some cases yes, but loose fuse holders can cause the fuse to get hot enough to melt the link.especially if the powder in the fuse
has settled from being in the same position for years on the
old fuses & you will notice the end of the fuse getting a
purplish color instesd of normal color.
-
11-24-2011, 06:39 AM #22
Professional Member
- Join Date
- Jun 2005
- Location
- Henrico,VA
- Posts
- 69
Update
I paid a return visit to this rtu this week and checked the
voltage,amps and for any bad wiring.The fuses were still good.
I just checked it out because the customer thought he was having
another problem.
What I did find this time was an unusual amount of heat in the fuse block area.In excess of 170F in some spots using my
infrared thermometer.
I removed the fuses and squeezed the holders tighter and replaced the sta-con female spade connectors for some horseshoe connectors and tightened these down under the fuse block screws.
Restarted the unit and the highest temperature was 90F.A.B.C.-always be careful!
-
11-24-2011, 06:58 AM #23
Nice. Loose connections are the devil. Glad you found something.