    Another question. Has anyone anywhere found a home with co in the living space and it was casued by a gas pack?

  2. #102
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by JonesHVAC-R View Post
    Are you saying that if a heat exchanger is cracked that CO will not get into the home?
    If there is CO getting into the home, the crack is the least likely culprit. In fact it is right up there with winning the lottery, just about impossible.

  3. #103
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Post Likes
    Quote Originally Posted by bigtime View Post
    Has anyone anywhere found a home with carbon monoxide in the living space, and the cause was a small crack in the furnace heat exchanger? If so Id like to hear the details.

    On any residential co problem, Id put my money on a vent problem. Spend more time inspecting vents...
    Actually, out of 4 calls this month I had 3 homes reading anywhere from 3-9ppm and 1 reading above 20ppm(shut furnace down before it got any higher). Out of those 4 two had cracked HX's. The one with 20ppm+ was carbon build up in the HX and the exhaust, customer upgraded anyway. The last one had a bad inducer assembly.

  4. #104
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by JonesHVAC-R View Post
    Actually, out of 4 calls this month I had 3 homes reading anywhere from 3-9ppm and 1 reading above 20ppm(shut furnace down before it got any higher). Out of those 4 two had cracked HX's. The one with 20ppm+ was carbon build up in the HX and the exhaust, customer upgraded anyway. The last one had a bad inducer assembly.
    What were the CO levels in the flue?

    Carbon buildup? That is just a symptom of a larger problem.

  5. #105
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    What were the CO levels in the flue?
    For which?

    Quote Originally Posted by chuckcrj View Post
    Carbon buildup? That is just a symptom of a larger problem.
    I agree, the furnace was 20+ years old and in a rental unit so I just recommended an upgrade to the landlord who agreed that would be most cost effective.

  6. #106
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by JonesHVAC-R View Post
    For which?


    .
    The ones with cracks.

  7. #107
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    If there is CO getting into the home, the crack is the least likely culprit. In fact it is right up there with winning the lottery, just about impossible.
    I agree the crack isn't the cause of CO developing... CO is caused from unburned fuel... The reason for the unburned fuel is what needs to be addressed. However, If you mix the two together the homeowner is looking at a very large expense as a hole or crack is definately a compromise and I don't know about you but I don't want my company liable by leaving a compromised HX in someones home and just fixing the reason for the unburned fuel... Just my honest opinion.

  8. #108
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    The ones with cracks.
    I'll have to pull the readouts of the combustion analyzer tomorrow, I'll let you know though.

  9. #109
    Join Date
    Nov 2008
    Location
    Northern California, foothills.
    Posts
    227
    Post Likes
    Uh, I gotta ask. So if you all agree that a crack in the heat exchanger doesn't pose a CO threat,
    then what's wrong with a crack in the heat exchanger? Please explain the "compromised".
    If it is all about some future threat, what threat is that and how long realistically before
    that threat would appear?

    (I'm lurking, not arguing. All of this is unfortunately new & puzzling stuff to me.)

  10. #110
    Join Date
    Nov 2008
    Location
    Northern California, foothills.
    Posts
    227
    Post Likes
    Wait. I have a contribution.
    On another thread, "where can I find west coast combustion analysis training?", I found
    a link to a 52 page PDF on Testo's website. On page 28, it talks about finding heat
    exchanger cracks and agrees that CO analysis won't change, but rather O2 levels
    will, or might. Fascinating stuff.
    So here again is the link:
    http://www.google.com/url?sa=t&rct=j...nOAgyjFgEodNXw

  11. #111
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    George the issue boils down to liability. Since none of us have a crystal ball and we can't tell when that crack is going to split open it's a CYA thing.

    When they do open enough to disrupt the flame large amounts of CO can be produced,soot forms causing the cell to not vent correctly and the CO then spills into the home. I recall one like that two winters ago. New customer that called because the CO detector was going off. They shut the furnace off then called us. I got there and fired up the furnace first to see if it was the source of CO and my analyzer showed 800ppm spilling out the front of the furnace yet the roll out switch was not tripping. The top of that cell was 100% blocked with soot and there was a crack that must have opened up as the exchanger heated.

  12. #112
    Join Date
    Jul 2012
    Location
    Cincinnati ohio
    Posts
    252
    Post Likes
    Quote Originally Posted by trouble time View Post
    A cracked heat exchanger can be a bad situation. But with the newer furnaces that are essentially negative pressure, is there any harm? Today I found a heat exchanger, 16 years old, very rusty on the inside with seems that are 1/8 to 1/4 inch separated. No indication of a crack, but it made me nervous just looking at it. I brought the customer down to the furnace and explained that although I could not find a definitive crack, my gut feeling is that if I pulled the furnace out, I would find one. I used the bore scope and could see signs overheating. I red tagged it.
    Questions. How far do you go to find a crack if you suspect one? What do you let go?
    We have guys at my company that will actually pull the h/x to show a customer a crack or rust hole. I personally just look with my camera and show the customer, explain there is no way of knowing when it will rust through and that I won't be there everyday to check. If its really bad its better to red tag it and cover your butt .

  13. #113
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Last crack I found was just last Friday and it was as hairline as you can get while still producing resistance when dragging a wire across it. I brought them both down and showed them how I shut the gas cock, turned the gas valve off and left the disconnect off. I fully explained to them the possible dangers of reversing my actions and ignoring the red tag. I also explain how CO is produced (incomplete combustion) and that a crack in the HE will not necessarily produce CO.

    The reason I take these steps? Simple. As this and multiple other lengthy threads in this forum (I spent most of the day reading them) and others clearly demonstrate: We as an industry haven't a clue as to WTF we are doing when it comes to this particular issue. My method demonstrates the best possible compromise I can negotiate between all I read. My company is covered and I am protecting my customer in as much as they will let me.

+ Reply to Thread
Page 6 of 6 FirstFirst 123456

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •