Thread: Cracked heat X ????

  1. #81
    Join Date
    Dec 2011
    Location
    Georgia
    Posts
    18
    Post Likes
    not to be argumentative but tell me what a "tight" crack is. and in what case have you found this type of crack and your monitor didn't get it? if so what numbers were you reading? what type of furnace? to me a crack of any size is going to show up if it is in the airstream. most hvac guys dont use monitors anyway so i understand the skeptics

  2. #82
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by CAtech1986 View Post
    not to be argumentative but tell me what a "tight" crack is. and in what case have you found this type of crack and your monitor didn't get it? if so what numbers were you reading? what type of furnace? to me a crack of any size is going to show up if it is in the airstream. most hvac guys dont use monitors anyway so i understand the skeptics
    I use a CA on every furnace I work on. Many many times I have found cracks in heat exchangers that showed zero change in O2 or CO when the blower starts.

    One particular model that comes to mind is the Lennox Duracurve heat exchangers. Every time I have found them cracked I have found it visually and they are always in the back on the first curve. They are never IME leaking air, at least not enough to pick up on an analyzer.

    If you are relying on only a CA to find cracks you will miss over 80% of them.

  3. #83
    Join Date
    Dec 2011
    Location
    Georgia
    Posts
    18
    Post Likes
    the lennox duracurve was a 80+ or natural draft?

  4. #84
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by CAtech1986 View Post
    the lennox duracurve was a 80+ or natural draft?
    You need to fill in your profile, are you a tech? I can't believe their are techs that have never seen a duracurve. They are all natural draft.

    My post above is true of all furnaces, I just used the duracurve as an example.

  5. #85
    Join Date
    Dec 2011
    Location
    Georgia
    Posts
    18
    Post Likes
    sorry just signed up. I am a tech. Been in the field five years. Frankly there are not a lot of natural draft furnaces left in my part of the country. most have been replaced. I still see them occasionally. i do enjoy being able to test seperate burners with the CA. Mostly oil, and induced draft i have experiance with. 90+ also of course. Had a Tappan a few years ago with 4000ppm in the exhaust before the draft hood with a draft of .07" i removed the draft hood completely and sealed it off. It is now using a 6" barometric and working great still today. other than that i reallyt don't see many nowadays. i would like to know how any furnace with a legitimate crack in the heat exchanger will not cause some kind of co action. if it is natural draft than the combustion chamber is subjected to a constant negative pressue. with any kind of hole in it the blower will cause some infiltration of what is otherwise supposed to be a sealed chamber. drastic changes... maybe, maybe not. 10-15 minutes of operation should reveal some sort of problem. especially as it gets hotter. O2 will drop, co will rise a classic venting diagnosis could become confused with a slight crack i suppose.

  6. #86
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Most of the time a leak allowing air to infiltrate the hx will cause the o2 to rise and the CO to fall when the blower comes on. Only a severe crack would cause the CO to rise.

    Kudos for learning how to use a CA. I also regularly remove draft hoods and install barometric draft controls.

  7. #87
    Join Date
    Dec 2011
    Location
    Georgia
    Posts
    18
    Post Likes
    wow! we should just start cracking heat exchangers and that will solve our carbon monoxide and venting problems!!!

  8. #88
    Join Date
    Dec 2011
    Location
    somewhere between here and there
    Posts
    478
    Post Likes
    goodman with the rings(gmp)

    lennox with the duracurve(whisperheat)

    bryant (394 GAD)

    oh how i lovew to do a tuneup on these....next thing u know the red tag comes out, and i leave the house with a $6000 job

    o how i love these

  9. #89
    Join Date
    Jan 2011
    Location
    Boston, MA
    Posts
    462
    Post Likes
    Quote Originally Posted by CAtech1986 View Post
    wow! we should just start cracking heat exchangers and that will solve our carbon monoxide and venting problems!!!
    uhh what?

  10. #90
    Join Date
    Dec 2011
    Location
    somewhere between here and there
    Posts
    478
    Post Likes
    Quote Originally Posted by CAtech1986 View Post
    The best way to identify a cracked heat exchanger is with a combustion analyzer. with gas pressure set at 3.5 for natural and 10-11" w.c for lp. you'll notice a rise in co when the blower comes on. a drastic rise. you don't need to pull it out or anything. if it is rusting that indicates there has been a problem for a long time. What type of furnace is it?



    the best way to identify a cracked htxchanger, is to be knowledgible in the specific models and where they crack, as i posted earlier....maybe wont get all of them...but using a CA is a poor way to find them...IMO

    whisperheats are all(ok 95%) cracked...with no diff using the CA.....if crack aint open...

    and IMO a crack is a crack is a crack. integrety is gone and unsafe to operate.

  11. #91
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Post Likes
    Curiousity getting the better of me..... how many of you use a CO meter (calibrated before entry to home) while doing clean and checks?

  12. #92
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by JonesHVAC-R View Post
    Curiousity getting the better of me..... how many of you use a CO meter (calibrated before entry to home) while doing clean and checks?
    All the top techs!

    I carry a CO meter on every call to alert me if I walk into a dangerous space.

    I do a combustion analysis on all gas or oil burning equipment I work on.

  13. #93
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    All the top techs!

    I carry a CO meter on every call to alert me if I walk into a dangerous space.

    I do a combustion analysis on all gas or oil burning equipment I work on.
    Lol, I agree there! Leads to my next question...

    How many of you when entering home and get a reading anywhere from 1-6ppm recommend replacing the furnace right there? (assuming the CO is coming from the furnace during operation)

  14. #94
    Join Date
    Dec 2011
    Location
    somewhere between here and there
    Posts
    478
    Post Likes
    lol...loaded question

    but yes... i do carry my co detector into every job.....responses from homeowners vary, but most are impressed


    Please, Please Please......keep the Factory Smoke in the Wires!!!!!


    Is it Rum'Oclock yet???

  15. #95
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by JonesHVAC-R View Post
    Lol, I agree there! Leads to my next question...

    How many of you when entering home and get a reading anywhere from 1-6ppm recommend replacing the furnace right there? (assuming the CO is coming from the furnace during operation)
    If the furnace is spilling CO and causing house levels anywhere above zero then yes new is the first choice. Usually there is a repair option as well if the HO can't afford new. (unless the HX is cracked, which is almost never the cause of CO getting into the home)

  16. #96
    Join Date
    Dec 2011
    Location
    Toronto
    Posts
    11
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    A rusted heat exchanger is not a failure if there is no "visible crack or hole".
    What type of heat exchanger is it? When you open up the supply duct and look at it are the seams folded and welded. Because those particular H/E are tanks and seem to last. With a bore scope through the burner section they look cracked but indeed they are not.

    I agree no visible crack or hole = No red tag

  17. #97
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    Quote Originally Posted by JonesHVAC-R View Post
    Curiousity getting the better of me..... how many of you use a CO meter (calibrated before entry to home) while doing clean and checks?
    Got a perfect example of why that's important today. Lennox G20 that another company replaced the heat exchanger last year. It had the typical stress mark and rust line along the back but passed water test. Cleaned the burners,crossovers,pilot assembly and flame sensor then put it back together to get some flue gas readings. Stuck the probe in the flue and had 4.2% O2 and over 9000 ppm of CO,I know should have pulled the probe out way before that to save the sensor. Gas valve was cranked all the way in and reading 7.2", backing it out didn't change the pressure. Installed a new gas valve and made a new sheet metal flange that the bone heads left out. CO 14ppm with 7.2 O2 after fixes.

  18. #98
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Post Likes
    Quote Originally Posted by martyinlincoln View Post
    Got a perfect example of why that's important today. Lennox G20 that another company replaced the heat exchanger last year. It had the typical stress mark and rust line along the back but passed water test. Cleaned the burners,crossovers,pilot assembly and flame sensor then put it back together to get some flue gas readings. Stuck the probe in the flue and had 4.2% O2 and over 9000 ppm of CO,I know should have pulled the probe out way before that to save the sensor. Gas valve was cranked all the way in and reading 7.2", backing it out didn't change the pressure. Installed a new gas valve and made a new sheet metal flange that the bone heads left out. CO 14ppm with 7.2 O2 after fixes.
    7.2"!! I had a tech once turn one down to 2" while I was away... I got back and asked why so low and he replied that is where it needed to be in order for the burners not to snuff out... Not quite sure what the hell he was thinking there... I told him to come with me and it turned out they weren't snuffing at all but they cutting out from the rollout sensor. Old Bryant 80% rooftop unit with just about everything rusting... gave them the option of repair or new unit, they took the new unit

  19. #99
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    If the furnace is spilling CO and causing house levels anywhere above zero then yes new is the first choice. Usually there is a repair option as well if the HO can't afford new. (unless the HX is cracked, which is almost never the cause of CO getting into the home)
    Are you saying that if a heat exchanger is cracked that CO will not get into the home?

  20. #100
    Join Date
    Dec 2003
    Posts
    2,851
    Post Likes
    Has anyone anywhere found a home with carbon monoxide in the living space, and the cause was a small crack in the furnace heat exchanger? If so Id like to hear the details.

    On any residential co problem, Id put my money on a vent problem. Spend more time inspecting vents...

+ Reply to Thread
Page 5 of 6 FirstFirst 123456 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •