    Trane Heat Pump Installation Problems

    If this is what you want to call DIY and don't wish to answer, please point me in the right direction

    I had this Trane 16i installed last November. The T-Stat settings were as shown. After calling them out 2 weeks later a different tech set the T-Stat as shown. You may see why I have little, to no, confidence in the installer. After
    several calls the installer refused to come out again but said my heating bills
    where normal for the weather.I went from a 2 ton ~11 sear system to a 16+ sear 2.5/3 ton unit and my electric bill went up over 30%. The AC part of this system seems to work great and my electric bill fell ~20%. I believe the strip heaters are coming on whenever the heat comes on. I'm not sure if it's a wiring or control problem and would like any advice you may want to give. I thought it would be easiest to check the T-Stat first. Thanks


    Compressor: 4TWX6036E1000A
    Air Handler: 4TEE3F40B1000B
    T-Stat: TCONT803
    Trane Cleaneffects


    Initial Install
    0170 12
    0200 1
    0210 0
    0220 1
    0230 1
    0260 5
    0280 0
    0300 1
    0310 3
    0320 0
    0330 2
    0350 40
    0380 0
    0500 0
    0510 0
    0580 5
    0600 90
    0610 50
    0640 12
    0650 0
    0660 0
    0670 0
    0680 2
    0690 2
    0700 0
    0710 0

    Corrected Settings
    0170 12
    0200 0
    0220 3
    0230 3
    0260 9
    0270 9
    0280 0
    0300 1
    0310 3
    0320 0
    0330 2
    0340 1
    0380 0
    0500 0
    0510 0
    0580 5
    0600 90
    0610 67
    0640 12
    0650 0
    0660 0
    0670 0
    0680 2
    0690 2
    0700 0
    0710 0

  2. #2
    Join Date
    Feb 2011
    Location
    North East Ohio
    Posts
    786
    If your energy bills for cooling are dropping and in heating are rising, I would bet that your electric heat is indeed coming on every time. Are you in a climate that is below 20 deg. for the entire winter? I would contact a contractor that is willing to work with you. Unfortunately that will come with a price tag, but so does your system being set up incorrectly. Good luck

  3. #3
    I'm in mid-lower Tennessee. Rarely gets to 20 but sometimes gets below zero for a short time.

  4. #4
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    0260 & 0270

    never have figured out why some people are bent on bringing the electric heat on "9" cph

    th8320 (+/-)=tcont803, if anyone else cares
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  5. #5
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,517
    i have to wonder are you setting the stat back during the day and then kicking up up 4 or ten degrees
    if so then you are kicking in the heaters to bring the temp up to with in 1 or 2 degrees of set point then the heatpump will take over and raise you elecrric bill acordingly
    a properly sized pump osnt ment to recover it is ment to maintain temp
    set and forget is the best way to save

  6. #6
    Join Date
    Jul 2004
    Location
    Charleston, SC
    Posts
    930
    Quote Originally Posted by dandyme View Post
    0260 & 0270

    never have figured out why some people are bent on bringing the electric heat on "9" cph

    th8320 (+/-)=tcont803, if anyone else cares
    CPH = Cycles Per Hour. This is the MAX # of cycles allowed in the control algorithm. Electric heat does not have a start up cost like a compressor motor, so cycle it as often as needed to do the job. I usually set this parameter to 12.

    Quote Originally Posted by tinknocker service tech View Post
    i have to wonder are you setting the stat back during the day and then kicking up up 4 or ten degrees
    if so then you are kicking in the heaters to bring the temp up to with in 1 or 2 degrees of set point then the heatpump will take over and raise you elecrric bill acordingly
    a properly sized pump osnt ment to recover it is ment to maintain temp
    set and forget is the best way to save
    Didn't see a setting for 530, Adaptive Intelligent Recovery. Set that to 1 to minimize Tinknocker's concern.

    Even with AIR enabled, I tell customers to not set the set-back temp more that 4* below normal temp in the heating mode. You really arent saving that much and the system may not be able to recover from a larger setback.
    "Customer Service" is not a department, it's an attitude!
    ???

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event