    Oct 2011
    Trane Heat Pump Installation Problems
    If this is what you want to call DIY and don't wish to answer, please point me in the right direction
    I had this Trane 16i installed last November. The T-Stat settings were as shown. After calling them out 2 weeks later a different tech set the T-Stat as shown. You may see why I have little, to no, confidence in the installer. After
    several calls the installer refused to come out again but said my heating bills
    where normal for the weather.I went from a 2 ton ~11 sear system to a 16+ sear 2.5/3 ton unit and my electric bill went up over 30%. The AC part of this system seems to work great and my electric bill fell ~20%. I believe the strip heaters are coming on whenever the heat comes on. I'm not sure if it's a wiring or control problem and would like any advice you may want to give. I thought it would be easiest to check the T-Stat first. Thanks
    Compressor: 4TWX6036E1000A
    Air Handler: 4TEE3F40B1000B
    T-Stat: TCONT803
    Trane Cleaneffects
    Initial Install
    0170 12
    0200 1
    0210 0
    0220 1
    0230 1
    0260 5
    0280 0
    0300 1
    0310 3
    0320 0
    0330 2
    0350 40
    0380 0
    0500 0
    0510 0
    0580 5
    0600 90
    0610 50
    0640 12
    0650 0
    0660 0
    0670 0
    0680 2
    0690 2
    0700 0
    0710 0
    Corrected Settings
    0170 12
    0200 0
    0220 3
    0230 3
    0260 9
    0270 9
    0280 0
    0300 1
    0310 3
    0320 0
    0330 2
    0340 1
    0380 0
    0500 0
    0510 0
    0580 5
    0600 90
    0610 67
    0640 12
    0650 0
    0660 0
    0670 0
    0680 2
    0690 2
    0700 0
    0710 0
    Feb 2011
    North East Ohio
    If your energy bills for cooling are dropping and in heating are rising, I would bet that your electric heat is indeed coming on every time. Are you in a climate that is below 20 deg. for the entire winter? I would contact a contractor that is willing to work with you. Unfortunately that will come with a price tag, but so does your system being set up incorrectly. Good luck
    Oct 2011
    I'm in mid-lower Tennessee. Rarely gets to 20 but sometimes gets below zero for a short time.
    0260 & 0270
    never have figured out why some people are bent on bringing the electric heat on "9" cph
    th8320 (+/-)=tcont803, if anyone else cares
    leland nc
    i have to wonder are you setting the stat back during the day and then kicking up up 4 or ten degrees
    if so then you are kicking in the heaters to bring the temp up to with in 1 or 2 degrees of set point then the heatpump will take over and raise you elecrric bill acordingly
    a properly sized pump osnt ment to recover it is ment to maintain temp
    set and forget is the best way to save
    Charleston, SC
    Quote Originally Posted by dandyme View Post
    0260 & 0270
    CPH = Cycles Per Hour. This is the MAX # of cycles allowed in the control algorithm. Electric heat does not have a start up cost like a compressor motor, so cycle it as often as needed to do the job. I usually set this parameter to 12.
    Quote Originally Posted by tinknocker service tech View Post
    Didn't see a setting for 530, Adaptive Intelligent Recovery. Set that to 1 to minimize Tinknocker's concern.
    Even with AIR enabled, I tell customers to not set the set-back temp more that 4* below normal temp in the heating mode. You really arent saving that much and the system may not be able to recover from a larger setback.
    "Customer Service" is not a department, it's an attitude!