Results 1 to 6 of 6
  1. #1

    sorry, Sensible pizza oven

    Sorry gents, SENSIBLE heat value for pizza oven in restaurant. 450 F and oven is in the conditioned space Thanks again

  2. #2
    Join Date
    Sep 2011
    Location
    Vancouver, WA
    Posts
    263
    What is the btu input of the pizza oven? I would start there first.

  3. #3
    Join Date
    Oct 2011
    Location
    NJ
    Posts
    149
    Under a hood or vented?

    Brick oven?

  4. #4
    Join Date
    Oct 2011
    Location
    NJ
    Posts
    149
    ASHRAE only gives a value for under a hood, so I think a hood will be required. The calculation of heat gain from the appliance is 130 btuh to the room per sqr feet of hearth opening. According to ASHRAE.

    So a 3x4=12 sqr foot hearth opening will have a heat gain of 1560 btuh.

    (ASHRAE rating for Oven (pizza) per sf of open hearth under a hood.)

  5. #5
    The oven is to be a showpiece in the restaurant. It is a clay oven covered in mosaic tiles. it is wood burning so the btu input is not available. I understand that it will be power vented

  6. #6
    Join Date
    Oct 2011
    Location
    NJ
    Posts
    149
    My calculation from ASHRAE should give you a pretty close result.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event