Results 1 to 6 of 6
    Oct 2011
    sorry, Sensible pizza oven
    Sorry gents, SENSIBLE heat value for pizza oven in restaurant. 450 F and oven is in the conditioned space Thanks again
    Sep 2011
    Vancouver, WA
    What is the btu input of the pizza oven? I would start there first.
    Oct 2011
    NJ
    Under a hood or vented?
    Brick oven?
    Oct 2011
    NJ
    ASHRAE only gives a value for under a hood, so I think a hood will be required. The calculation of heat gain from the appliance is 130 btuh to the room per sqr feet of hearth opening. According to ASHRAE.
    So a 3x4=12 sqr foot hearth opening will have a heat gain of 1560 btuh.
    (ASHRAE rating for Oven (pizza) per sf of open hearth under a hood.)
    Oct 2011
    The oven is to be a showpiece in the restaurant. It is a clay oven covered in mosaic tiles. it is wood burning so the btu input is not available. I understand that it will be power vented
    Oct 2011
    NJ
    My calculation from ASHRAE should give you a pretty close result.
Comfortech365 Virtual Event
