    run time of current system

    Manual J says I need a 2.5 ton. I currently have 4 ton. Is there a way to time the cycle of my current system with a set point and outside temp to tell if I am currently over sized?

  2. #2
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,721
    on the hottest day of the year did your unit cycle on and off several times

  3. #3
    Join Date
    Jul 2005
    Posts
    5,576
    There's a way to ball park it. Assume that your unit is maintaining an indoor/outdoor temperature difference of 10. You clock the run times and find that the unit is running about 20 minutes out of the hour, or 33.33% of the time. Assuming that the heat load is proportional to the indoor/outdoor temperture difference, the unit would theoretically be able to maintain an indoor/outdoor difference of

    10/(33.33/100) = 30

    if it were to run nonstop.

    In reality the capacity of the system drops off as the ambient temperature increases, however the load isn't strictly propotional to the temperature difference either. The heat load does not increase at as great a rate as the temperature difference, so these two factors tend to cancel each other out to some extent.

    This will be nowhere near exact, but if you find that your system is grossly oversized using this method, then it probably is grossly oversized in reality.

  4. #4
    Join Date
    Feb 2010
    Location
    Cal
    Posts
    1,596
    You are late to the party blue, follow the link.
    Good luck.

    http://hvac-talk.com/vbb/showthread.php?t=869162

  5. #5
    Join Date
    Jul 2005
    Posts
    5,576
    Quote Originally Posted by btuhack View Post
    You are late to the party blue, follow the link.
    Good luck.

    http://hvac-talk.com/vbb/showthread.php?t=869162
    I remember that thread. A lot of good points raised. It would probably be more accurate to clock the runtimes on the hottest days. The percent runtime method would, for some not so obvious reasons, be more accurate at higher indoor/outdoor temp differences. I probably wouldn't try it with a temp difference below 15.

  6. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,806
    Quote Originally Posted by electricblue View Post
    Manual J says I need a 2.5 ton. I currently have 4 ton. Is there a way to time the cycle of my current system with a set point and outside temp to tell if I am currently over sized?
    Think about it.

    Is it more likely that a manual J is incorrect, or a rule of thumb used to size your current system?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  7. #7
    Join Date
    Jun 2011
    Location
    Wake Forest, NC
    Posts
    352
    Quote Originally Posted by timebuilder View Post
    Think about it.

    Is it more likely that a manual J is incorrect, or a rule of thumb used to size your current system?
    We are assuming that the Manual J was done correctly. I have seen some really screwed up design parameters that have produced totally whacky load calculations.

    So long as the calculation was done correctly, then go with that. If you aren't sure about the load calc, call another company and ask them to do one for you so you can compare results. Be prepared to pay for their time if you want to see the load calculation report.
    It's not rocket-science...

    It's electromechanical thermodynamic engineering

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event