    Confused Heat Pump Mystery

    I'm writing to see if anyone can help solve a mystery regarding Heat Pumps.
    I have a two story house with 2, 2-ton Lennox Heat Pumps. I have owned the house for nearly 2 years and have noticed some efficiency problems. I have had the units serviced (no problems) and embarked on some research into why the units run all the time and cost a fortune to operate even with the thermostat set on 79 or 80.

    Here's what I found. Some of the research involved multiple units being installed too close together. I measured the distance between mine and it is at about 8". That seemed close to me - so I called a local hvac contractor and was told that 8" shouldn't make a difference in the efficiency of the units. I decided to contact the manufacturer, Lennox to get their thoughts on the matter. I was told by their consumer affairs folks that most definitely having only 8" between the units would negatively effect their efficiency. They said that they recommend 24" between multiple units (and that was substantiated by the fact that it is in the engineering data for the model).

    Puzzled, I called another HVAC contractor that I have used in the past (40 years of experience) and he said that "while he wouldn't say separating the units wouldn't help the problem, he didn't think it would solve it entirely". In my discussion with the Lennox rep, he said that being so close together, the units are essentially "competing for air". It is widely known and accepted that you are not supposed to obstruct hvac equipment. So, how could it not be an issue that an entire air intake surface of each unit are 8" apart? Additionally, if they are both running simultaneously, wouldn't they both be trying to draw in air on the obstructed sides and "fighting against each other"
    so to speak?

    I would greatly appreciate some professional insight into the matter. I understand that hvac contractors and engineers have completely different perspectives - but they can't both be right about this!

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,093
    Post Likes

    You have figured it out

    Quote Originally Posted by wer525 View Post
    I'm writing to see if anyone can help solve a mystery regarding Heat Pumps.
    I have a two story house with 2, 2-ton Lennox Heat Pumps. I have owned the house for nearly 2 years and have noticed some efficiency problems. I have had the units serviced (no problems) and embarked on some research into why the units run all the time and cost a fortune to operate even with the thermostat set on 79 or 80.

    Here's what I found. Some of the research involved multiple units being installed too close together. I measured the distance between mine and it is at about 8". That seemed close to me - so I called a local hvac contractor and was told that 8" shouldn't make a difference in the efficiency of the units. I decided to contact the manufacturer, Lennox to get their thoughts on the matter. I was told by their consumer affairs folks that most definitely having only 8" between the units would negatively effect their efficiency. They said that they recommend 24" between multiple units (and that was substantiated by the fact that it is in the engineering data for the model).

    Puzzled, I called another HVAC contractor that I have used in the past (40 years of experience) and he said that "while he wouldn't say separating the units wouldn't help the problem, he didn't think it would solve it entirely". In my discussion with the Lennox rep, he said that being so close together, the units are essentially "competing for air". It is widely known and accepted that you are not supposed to obstruct hvac equipment. So, how could it not be an issue that an entire air intake surface of each unit are 8" apart? Additionally, if they are both running simultaneously, wouldn't they both be trying to draw in air on the obstructed sides and "fighting against each other"
    so to speak?

    I would greatly appreciate some professional insight into the matter. I understand that hvac contractors and engineers have completely different perspectives - but they can't both be right about this!
    The hvac contractor has given you bad information, the units need to dissipate the heat that is being absorbed inside of the structure.

  3. #3
    Join Date
    Oct 2011
    Posts
    4
    Post Likes
    Thread Starter
    Thanks for your response. Forgive my layman's question, but do you mean the units dissipate heat inside the unit itself or by structure do you mean the heat they absorb from the home? If you mean inside the units, the 8" space between them would compromise their ability to to that? Thanks again!

  4. #4
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,093
    Post Likes
    Quote Originally Posted by wer525 View Post
    Thanks for your response. Forgive my layman's question, but do you mean the units dissipate heat inside the unit itself or by structure do you mean the heat they absorb from the home? If you mean inside the units, the 8" space between them would compromise their ability to to that? Thanks again!
    In the cooling mode your unit would absorb the heat inside your house and would need to reject it out side. If the units are restricted by being to close to each other or a fence, wall, plants etc. the heat will not be rejected from the refrigerant in the system as it should, and will lead to performance issues and failures.

  5. #5
    Join Date
    Oct 2007
    Location
    Austin Texas
    Posts
    1,933
    Post Likes
    Picture a heavy set guy running a marathon and all he can breathe through is a soda straw. That is the best analogy I can think of for your situation.
    Nemo me impune lacessit.

    How much blood do I have to bathe in to get clean?

    Don't look down on anyone unless you're helping them up.

  6. #6
    Join Date
    Jun 2011
    Location
    Wake Forest, NC
    Posts
    353
    Post Likes
    Based on what you have told us thus far I would agree with the second contractor you spoke to. It is always advisable to install equipment according to manufactures specs. If they say 24", then 24" is the ideal. That being said, two units installed 22" apart probably would be fine... 8" is a bit tight, and the two units are competing for air, but I would not think this is 100% of the problem if they cannot keep up even with the thermostat set to 79 or 80. Before you go moving equipment at a high cost for little efficiency return consider the following:

    Find a pro you trust.

    Have them check
    1. Airflow: Look for obsructions in the supply or return air distribution system. Have the coil cleaned if needed, and have them determine the cfms your system is operating at.
    2. Static pressure: Have them perform a esp test to determine the return static, supply static, and then calculate the static of the air handler to determine if the design of the ductwork is restricting airflow
    3. Have a superheat/subcooling reading taken to verify proper refrigerant charge and balancing of the system.

    I suspect that if those items are done another, more obvious cause will be found, and then a real solution can be proposed either as an independent solution or in concert with moving one or both of the condensers.
    It's not rocket-science...

    It's electromechanical thermodynamic engineering

  7. #7
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,699
    Post Likes
    Consumer Affairs ( whomever the mfg is) only knows what they can read.

    there are mfg's that do have engineering literature that will permit units to sit as close to each other as 8"

    I'd venture you have other issues


    Engineering/Technical Representative would have more detail as to the proximity
    of units to each other
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  8. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    27,874
    Post Likes
    If the units were designed to force hot air out through the sides, then you would have an identifiable problem. A contractor with a flow hood can compare the airflow out the top of one unit when only one is running to the flow when both are running. That will tell you if you need to move a unit.

    From a standpoint of aerodynamics, I would expect enough air to be drawn in through the 8" gap to be able to satisfy whatever the flow rate is on a typical fractional horsepower condenser fan motor.

    You need to have the system checked. My money is on duct leakage and whether the duct design meets the needs of the rooms it serves.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. #9
    Join Date
    Apr 2001
    Location
    San Antonio, TX
    Posts
    2,217
    Post Likes
    From a service stand point a complete walk around would be nice. But you asked about efficiency, what are your KWH per day, per month, should be on your bill. When you say they run all the time, both or one more than other, does your stat tell you run times, are you or someone home all day?
    Have them serviced, on a day that ac is actually needed, the tech could check pressures on both units at same time both on then one off. Compare readings.

    Since you are only talking one side of unit they both will get about same amount of air but when one shuts down the other could bring in any excess heat from other, which may be bad, a tech should be able to eliminate this as the real problem.
    Breeze

  10. #10
    Join Date
    Oct 2011
    Location
    south al.
    Posts
    124
    Post Likes
    definately seperate the units by at least 18 more inches but i would suggest a load be done on the house floor by floor and also check the equipment to find out if they are performing to full efficiency. sounds to like other issues than just to close.

  11. #11
    Join Date
    Mar 2011
    Location
    Galveston Texas
    Posts
    530
    Post Likes
    We have multiple units that sit this close together all over down here. In our area many of the condensers are on platforms and were built for small inefficient units, and as the units gained efficiency and size the room on the platforms shrunk.

    this may hurt the actual functional efficiency of the units but not anything noticeable. You have other issues that should be addressed prior to worrying about the 8" space. Check ductwork, check static pressures, check for cleanliness of the coils. Much as everyone else has said.

  12. #12
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,486
    Post Likes
    my question is... how does something pass code like that?

    anyways. amm certain that the installation instructions have minimum clearences for those units clearly labeled in the first few pages, and should be followed.

    is there anything above these units as well? like a deck? lol

    as far as having them "maintenanced" well, that's open for interpretation as well... hopefully that maintenance includes chemically cleaning the outdoor coils...

    i can see where 8" of seperation would cause high operating pressures, and poor performance. sure wouldn't hurt to meet the manufacturers guidlines IMO
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

  13. #13
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,015
    Post Likes
    sorry clicked the wrong one.....

    there are alot more factors too. I have a customer that has 2 units side by side, with manufacturer's clearances supported.....But he built two 6 ft privacy fences to hide them on either side (front is open). On a 85 degree day, its about 114 degrees down by the condensers.
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.