    Quote Originally Posted by mr hottstepper View Post
    NOPE theres no exchanger on the condenser frame actually looked to see if it had one cause i had to do the same with a carrier XRV centrifugal last year but it was 134a not vaccum. i even inspected the rapture guard ,cuz that has a way of spoiling a good day.
    Quote Originally Posted by klove View Post
    No offense intended. I wish you the best of luck in figuring out where your problem lies.


    NO PROB DUDE, i jus needed some insight in the low pressure side of the system cause i saw so many potential problems and i'm not that much of a low pressure chiller guy

  2. #42
    Join Date
    Jul 2008
    Location
    LOS ANGELES
    Posts
    24
    Post Likes
    you said there was another trane of the same model/ser does it have the same purge to compare ? do you have a low pressure pumpout unit handy and a recovery drum..... have you leak tested not just by purge count? consider a new purge or a REDI PURGE sorry i keep reading post again , verify cond flow delta p, do a gpm calc & compare to design if you can get it

  3. #43
    Join Date
    Oct 2011
    Location
    New Hampshire
    Posts
    22
    Post Likes
    Have you let the machine sit and checked pressures? Possible someone added R-11?

  4. #44
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    185
    Post Likes
    Check the purge valves and make sure they are open. Sounds obvious but someone could have serviced the purge and left them closed. Clogged orifice or closed pump out solenoid will cause the suction temperatures to remain low if the tank is full of air. When you brushed the tubes did you check them for scale? What's the saturated condenser temperature? The attached PDF has an trouble shooting guide that will show you were to take your readings and what they should be.

  5. #45
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Quote Originally Posted by mr hottstepper View Post
    NO PROB DUDE, and i'm not that much of a low pressure chiller guy

    These are the key words in all of this thread
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  6. #46
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    213
    Post Likes
    Thread Starter
    Quote Originally Posted by Phisher View Post
    Check the purge valves and make sure they are open. Sounds obvious but someone could have serviced the purge and left them closed. Clogged orifice or closed pump out solenoid will cause the suction temperatures to remain low if the tank is full of air. When you brushed the tubes did you check them for scale? What's the saturated condenser temperature? The attached PDF has an trouble shooting guide that will show you were to take your readings and what they should be.
    the valves were open, i headin back down to the sight tomorrow so ill be sure to use all the info i got thanks for the serv bulletin especially, and thank you every body else let you guy know how it goes tomorrow

  7. #47
    Join Date
    Oct 2009
    Location
    USA
    Posts
    66
    Post Likes
    Don't forget what I said. Inspect the compressor for worn out valves. additionally; it was common for the expansion valve to plug up with sludge. When this happens the compressor becomes a vacuum pump and it's toast as well. My vote (from 17 years at Trane) bad condensing unit. This is a long distance diagnosis mind you

  8. #48
    Join Date
    Mar 2011
    Posts
    279
    Post Likes
    Quote Originally Posted by mr hottstepper View Post
    the valves were open, i headin back down to the sight tomorrow so ill be sure to use all the info i got thanks for the serv bulletin especially, and thank you every body else let you guy know how it goes tomorrow
    I'm guessing your in Trinidad and Tobago, West Indies? Trane Service in Miami has techs that travel the Caribbean. I suggest giving them a call and having a tech go down to check this machine out for you. They could probably have it figured out in under an hour. If you need the phone number send me a PM.

    You could also call Trane Puerto Rico, they could send someone down also, but I don't know their level of expertise.

  9. #49
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    213
    Post Likes
    Thread Starter

    Thumbs up

    Quote Originally Posted by mr hottstepper View Post
    THE manual guage is reading the same. Purge compressor running its jus not pumping out which means there iss no air but still, the hi pressure issue is still there, this morning it was 92f, water temp was 51 dropped setpoint to 46 wen system loads pressure gradualy goes up to 16 and cut off on hi press cutout. i really dont hav much experience with the purge unit changed the purge drier yesturday incase it was saturated, at this point im totally lost
    well i went back to the site today and met the unit purging on its own i loaded it up and condenser pressure is 13.5, 95% current and system is purging , .so according to the service bullitin "after you change the drier wait 72 hours to allow system to remove moisture properly",so the drier was definately saturated .. (i saw that a little to late) as luck would have it today is the 3rd day since i installed the drier. guys im so sorry for wasting your time ,but i thank you soo much for all the help and advice you gave me, if any of yall ever comin to d caribbean holla at me ill hook u guys up good ..

  10. #50
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    213
    Post Likes
    Thread Starter
    now its onto changing out the bearings on the other cvhe, any body got a manual for that by chance? although i think trane might send a bullitin with the bearings, but i wanna change the seals in it as well , can or if u dont have a manual can any of u guys tell me if the seal to impeller clearences are the same as the cvhf?

  11. #51
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    213
    Post Likes
    Thread Starter
    Quote Originally Posted by TheChillerMan View Post
    I'm guessing your in Trinidad and Tobago, West Indies? Trane Service in Miami has techs that travel the Caribbean. I suggest giving them a call and having a tech go down to check this machine out for you. They could probably have it figured out in under an hour. If you need the phone number send me a PM.

    You could also call Trane Puerto Rico, they could send someone down also, but I don't know their level of expertise.
    i cant seem to private message ill e-mail u

  12. #52
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes


    This was / is a good thread!!

    1.Condenser pressure 116*= 13.5psig

    2.So by leaving water temp converted to psig 96*=4.6psig

    3.Equals = 8.9psig



    I did not realize that leaving water temp was used
    to determine if air was present.
    Last edited by milkyway; 09-03-2012 at 11:00 AM. Reason: Adding
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  13. #53
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by milkyway View Post


    This was / is a good thread!!

    1.Condenser pressure 116*= 13.5psig

    2.So by leaving water temp converted to psig 96*=4.6psig

    3.Equals = 8.9psig



    I did not realize that leaving water temp was used
    to determine if air was present.
    Leaving water temperature is not used to determine if air is present. Leaving water temperature is used to determine condenser approach. 'Higher condenser approaches' means some things and 'lower condenser approaches' mean other things. Low condenser approach means that the tubes are not particularly fouled and that you have good heat transfer. If you have good heat transfer, then you probably aren't low on charge and that your high condenser pressure is probably due to air in the chiller. If you had high condenser pressure AND a high condenser approach temperature then (perhaps) you are low on charge or your tubes are fouled. Remember that all equipment is in the process of degrading in performance. They all have some degree of fouled tubes, non-perfect charge, non-condensibles, etc. You START with the biggest problems and work down until you get a satisfactory piece of equipment.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

+ Reply to Thread
Page 3 of 3 FirstFirst 123

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •