    got a cvhe 320 and purge unit temps are like 72, 60 degrees f for the lowest wenever system tries to fully load it shuts off on hi pressure purge is not comin on (cuz temp is above 22) but what can cause this to happen sensors are reading ok i check it with another tester and the probes are ok, i even went as far as to add some refrigerant yesturday , this made it worse of course any advice?

  2. #2
    SFTB is offline Bad email address, please contact Admin to fix
    Join Date
    Sep 2011
    Posts
    18
    Post Likes
    I would put a gauge on condenser and verify that pressure is actually higher than panel reads when running. Its hard to say if there's air with limited info. When you say purge isn't coming on does that mean not pumping out? All I can say is if the purge is running and suction temp is not dropping then possibly purge TXV could be bad. Subcooling could prove that. I suspect purge valves are open from what you state. Verify there is air and submit more info.

  3. #3
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    212
    Post Likes
    Thread Starter
    THE manual guage is reading the same. Purge compressor running its jus not pumping out which means there iss no air but still, the hi pressure issue is still there, this morning it was 92f, water temp was 51 dropped setpoint to 46 wen system loads pressure gradualy goes up to 16 and cut off on hi press cutout. i really dont hav much experience with the purge unit changed the purge drier yesturday incase it was saturated, at this point im totally lost

  4. #4
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    493
    Post Likes
    is likely to have moisture refrigeration system purge unit, the temperature should be 22 F suction temp unit purge air to condense

  5. #5
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    212
    Post Likes
    Thread Starter
    so ure saying that althought the suction temp is 92degf , and condensing pressure on unit is high the purge unit is workin ok?.
    i now remembered something i didnt check to see if the purge is undercharged, don't have my ir meter today so i cant check sub cooling .Question if purge unit is short on refigerant for some reason will i get this , highpressure problem and will purge temp be high as well?

  6. #6
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,142
    Post Likes
    You say that at this point you are totally lost. I agree. Your problem is high pressure, yet you have not given any info concerning saturated condenser refrigerant temperature, or entering and leaving condenser water temperatures, or entering and leaving condenser water pressures. In other words, your problem may not be with the purge unit. I can't tell from here because I don't see where you have verified the presence of air. You should have a qualified tech take a look at it.

  7. #7
    Join Date
    Nov 2008
    Posts
    380
    Post Likes
    Shut the valves going to the purge and it should pump out in a few minutes.

    Before you do that put your hand on the discharge line of the purge compressor and see what the temp. is. It should be very hot with the suction temp. that you listed for the purge.

    Be very careful fooling around with the charge in the purge as it is only a few ounces.

    Take sat. cond. temp. convert to pres. and compare to actual cond. pres. to tell if air is in machine.

    Also check cond. water flow rate.

  8. #8
    SFTB is offline Bad email address, please contact Admin to fix
    Join Date
    Sep 2011
    Posts
    18
    Post Likes
    I think the past couple replies are in the right direction and I agree with their suggestions. I don't recommend checking subcooling with an infrared because of copper's emmisivity which has to do with its reflective properties. I would use a probe. The liquid line on a purge, provided its a trane, is 1/4 " or smaller. If you have to check copper with a infrared I would spray paint it black first. May have to check discharge temp to liquid temp to trouble shoot purge because I don't think they come with a pressure access unless you add it.

  9. #9
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    212
    Post Likes
    Thread Starter
    Quote Originally Posted by Nuclrchiller View Post
    You say that at this point you are totally lost. I agree. Your problem is high pressure, yet you have not given any info concerning saturated condenser refrigerant temperature, or entering and leaving condenser water temperatures, or entering and leaving condenser water pressures. In other words, your problem may not be with the purge unit. I can't tell from here because I don't see where you have verified the presence of air. You should have a qualified tech take a look at it.

    here are the readings,
    evap pressure 16hg
    cond press-13.5psig
    chwe-58degf diff 9degf
    chwl-51degf
    con-in-96degf
    con-out-86degf diff 10degf
    current limit setpoint is 81%
    water temp set at 50degf

    but my question still remains why isnt purge unit picking up non condensables and purging on its own? ill check the sub cooling thursday wen i go back there

  10. #10
    Join Date
    Mar 2011
    Posts
    274
    Post Likes
    Quote Originally Posted by mr hottstepper View Post
    here are the readings,
    evap pressure 16hg
    cond press-13.5psig
    chwe-58degf diff 9degf
    chwl-51degf
    con-in-96degf
    con-out-86degf diff 10degf
    current limit setpoint is 81%
    water temp set at 50degf

    but my question still remains why isnt purge unit picking up non condensables and purging on its own? ill check the sub cooling thursday wen i go back there
    because there may not be any non-condensables!

    Are you sure about your entering condenser water temp and leaving condenser water temp?

    96* entering water would probably cause your high condenser pressure.

    You also need to check entering and leaving condenser water PRESSURE. What is the pressure differential? Too low flow will also cause high condenser pressure.

    Is the chiller surging?

    What are the approaches?

  11. #11
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    493
    Post Likes
    that coolant is 123 or 11. which is the temperature of saturated cond gives all possible information in advance by the pressure of the condenser air in the system appears

  12. #12
    Join Date
    Mar 2011
    Posts
    274
    Post Likes
    Quote Originally Posted by servicetrane View Post
    that coolant is 123 or 11. which is the temperature of saturated cond gives all possible information in advance by the pressure of the condenser air in the system appears

    I'm guessing your first language isn't English.

  13. #13
    Join Date
    Jan 2011
    Location
    tt, west indies
    Posts
    212
    Post Likes
    Thread Starter
    Quote Originally Posted by servicetrane View Post
    that coolant is 123 or 11. which is the temperature of saturated cond gives all possible information in advance by the pressure of the condenser air in the system appears

    yup its r123