    Confused Duct leakage in cooling loads

    For construction in the last decade, Houston region, does it seem plausible to professionals that duct leakage would account for 3% of cooling loads? I always thought average duct leakage was higher, even for Energy Star homes built 2002-07. And thought with higher duct leakage, surely would be responsible for more than 3% of cooling loads. This is Houston TX and the vast majority of houses have ducts and equipment in unconditioned attics.

    Thanks for your thoughts -- Pstu

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Not sure where you got the 3% from but it can and usually is much greater than that.

  3. #3
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,361
    The default duct heat gain and air leakage for Manual J v7 is 15%. This has worked well. I believe that they also had fudge factors built in to make it work. Thus the real allowance was higher than 15%. My guess is 20% or more.

    The DOE says 25 to 40% and may be more if the ducts are in an attic. http://www.eere.energy.gov/buildings...s/db/34122.pdf
    See Page 7 in the PDF file or page 2 in the document.
    "I have never let my schooling interfere with my education."
    Mark Twain
    More at: http://www.quotationspage.com/subjects/education/

  4. #4
    Join Date
    Jun 2011
    Location
    Wake Forest, NC
    Posts
    352
    3% would be sweet! But no, it is much higher than that.
    It's not rocket-science...

    It's electromechanical thermodynamic engineering

  5. #5
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304

    Exclamation

    The source of the 3% number is from this study:

    http://www.advancedenergy.org/buildi...ency_Study.pdf

    Right there on page 3 it makes this statement. I am very curious how a professional study can say something so contrary to what I have learned over the years.

    As I read it, the study makes a big thing about how Energy Star homes have tight building envelopes, low duct leakage, etc. And that there are many houses built close to ES standards, which do not have the formal label. I never thought ES criteria was exceptional, just definitely above average.

    The homes were from Harris, Brazoria and Montgomery counties. For some reason they left out the fast growing Fort Bend county immediately to the west. I was always under the impression that only a few of our municipalities enforced good building practices, and out in the counties there was no enforcement and therefore builders said no rules were applicable. You hear that a lot around here, that you are lucky to get any kind of conscientious craftsmanship.

    Hope this helps -- Pstu

  6. #6
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,361
    Quote Originally Posted by pstu View Post
    The source of the 3% number is from this study:

    http://www.advancedenergy.org/buildi...ency_Study.pdf

    Right there on page 3 it makes this statement. "the study team found that the REM/Rate projected average cooling load of 5,506 kWh/yr was 3 percent higher than the billing analysis average cooling load of 5,677 kWh/yr." I am very curious how a professional study can say something so contrary to what I have learned over the years...
    I think REM/RATE is a standardized form used to collect the calculated heat load details. Their claim is not about duct leakage but about the accuracy of the projected cooling energy use compared to actual usage for a large group of homes. They are patting themselves on the back and a measure of skepticism is in order.
    "I have never let my schooling interfere with my education."
    Mark Twain
    More at: http://www.quotationspage.com/subjects/education/

  7. #7
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304
    While they do say what you quoted, the one I was dwelling on said "Building envelope leakage appears to be responsible for about 14 percent of summer/cooling loads while duct leakage only appears to account for about 3 percent of summer/cooling loads."

    There is a variance between the PDF page number and the one labeled at the bottom of each page, which causes confusion. The above quote is labelled page 3 by the authors, while it is probably page 8 according to the Adobe program. I regret not making that clearer.

    Thanks -- Pstu

  8. #8
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,361
    Duct leakage is a specific kind of envelope leakage that is fan driven. I have no idea how they determined how to split out duct leakage from the rest of the envelope leakage.

    The DOE document is more realistic in my opinion, unless Houston code enforces that ductwork be installed inside of the building envelope or enforces exterior duct sealing with mastic during construction. Do they?
    "I have never let my schooling interfere with my education."
    Mark Twain
    More at: http://www.quotationspage.com/subjects/education/

  9. #9
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304
    Houston is pretty much the "Wild West" of home construction. Only a few Municipalities have rules regarding duct leakage, e.g. Katy which is outside the survey area. In most regions builders rationalize that rules don't really exist because there is no enforcement staff. For the most part dirt is cheap and people expect houses to be also. Ducts inside conditioned space are really exceptional, the vast majority have all ducts and equipment in an unconditioned attic.

    Hope this helps -- Pstu

  10. #10
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,281
    The typical ENERGY STAR home must pass a minimum of two field tests – duct and house envelope leakage testing – to ensure that actual construction performance matches the computer modeling in terms of house envelope leakage and
    duct leakage.
    Building envelope leakage appears to be responsible for about 14 percent of
    summer/cooling loads while duct leakage only appears to account for about 3 percent of
    summer/cooling loads
    .....
    The rated homes duct leakage is % of total load not % of a/c
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  11. #11
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,361
    Quote Originally Posted by energy_rater_La View Post
    ...Building envelope leakage appears to be responsible for about 14 percent of summer/cooling loads while duct leakage only appears to account for about 3 percent of summer/cooling loads..
    So is the total leakage 14% including duct leakage, or 17% including duct leakage? Is this tested at CFM50 for both?
    "I have never let my schooling interfere with my education."
    Mark Twain
    More at: http://www.quotationspage.com/subjects/education/

  12. #12
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,369
    Quote Originally Posted by pstu View Post
    While they do say what you quoted, the one I was dwelling on said "Building envelope leakage appears to be responsible for about 14 percent of summer/cooling loads while duct leakage only appears to account for about 3 percent of summer/cooling loads."

    There is a variance between the PDF page number and the one labeled at the bottom of each page, which causes confusion. The above quote is labelled page 3 by the authors, while it is probably page 8 according to the Adobe program. I regret not making that clearer.

    Thanks -- Pstu
    What they may be forgetting is that duct leakage can accelerate building leakage.

    I SERIOUSLY DOUBT the average Texas flexductomaticflyingspaghettimonster install leaks on average 3% of all air moved into or out of the ducting. Are you kidding me? Folks who write these articles or conduct their studies need to get out into the field more and actually witness and measure what's going on.
    • Electricity makes refrigeration happen.
    • Refrigeration makes the HVAC psychrometric process happen.
    • HVAC pyschrometrics is what makes indoor human comfort happen...IF the ducts AND the building envelope cooperate.


    A building is NOT beautiful unless it is also comfortable.

  13. #13
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,361
    Shophound when you say, "Texas flexductomaticflyingspaghettimonster", are you Texans claiming credit for this travesty of ductwork?
    "I have never let my schooling interfere with my education."
    Mark Twain
    More at: http://www.quotationspage.com/subjects/education/

Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event