    charging 410a split on a cold day

    Any ideas on how to properly charge a 3 ton 13 seer york straight air unit on a brisk day? The unit is equipped with a piston, yes a piston. They recommended charging by superheat but the ambientt o/a temp was too low to intersect the chart on the outdoor panel. I had to get it running so i drove the head up until i got about 16 deg. S.h. I wasnt real happy leaving it that way. Any suggestions?

  2. #2
    Join Date
    Oct 2007
    Location
    Southern Indiana
    Posts
    94
    weigh it in

  3. #3
    Join Date
    Oct 2008
    Location
    Nashville ,TN
    Posts
    196
    Ball park is about all you can do until you have a load. Sucks but you should recheck on a warmer day. But In the real world that's about all you can do imo.

  4. #4
    Join Date
    Oct 2008
    Location
    Nashville ,TN
    Posts
    196
    Weigh it on package and splits check how much condenser charge per ft.

  5. #5
    Join Date
    Aug 2011
    Location
    Ontario
    Posts
    372
    How long is the line set and what size ??

  6. #6
    15 ft lineset approx. not including i.d. coil.

  7. #7
    3/8 -3/4 3 ton. Came with 15 ft of charge. Just wasnt satisfied due to low ambient & low load.

  8. #8
    Join Date
    Feb 2010
    Location
    Landis North Carolina
    Posts
    528

    charging heatpump in heating

    seeb my thread,charging heatpump in heat mode.

  9. #9
    Join Date
    Feb 2008
    Location
    Ontario, Canada
    Posts
    40
    I would do it right. You don't want to risk HO running an overcharged unit. Why piston?

  10. #10
    Thats what the engineer called for. I questioned the piston too but they didnt care. The condensor was feeding a fcu. It was in an industrial setting.

  11. #11
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    31,733
    York uses a piston. Only trouble with weighing in is you have to ASS-U-ME that the factory got the original charge right which I never believe. Get it close and check it again in warm weather. Got some kind of low ambient control on it? Crankcase heater? 3 ton is probably a recip.

  12. #12
    Join Date
    Feb 2008
    Location
    Ontario, Canada
    Posts
    40
    Oh right. I know what you mean. Engineers don't like to be questioned by us, who actually do the work and have a deep understanding of how things work. LOL

  13. #13
    Scroll compressor, low ambient, & crankcase r. all on it. I guess i will bug the foreman fitter to allow me to go back when its warmer (if there sre any warm days left) N.E.Pa. thanks forr everyone 's input.