Thread: Static Pressure.

  1. #21
    Join Date
    Jun 2011
    Posts
    34
    Post Likes

    Static

    I was told that esp should be taken distance of 2.5 times the diameter of the blower wheel from the center of the blower shaft.

  2. #22
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    As a general rule, you're right

    Quote Originally Posted by JBM1000 View Post
    Attachment 216462Before the coil period, and as close to a good center of R/Air at heater cabinet with filters installed. Your after the fan wheel input and output with a ****Wet Evap Coil****. This is full load evaluation at the home installed instead of just a factory chart. Remember Factory charts are bench test best guides to help the tech, it's up to you to make a real on site decision of many factors like supply vents closed and furniture to low to allow stratification of airflow, returnable airflow to the return grills and many many more more only real world experience techs finally learn home to home new or used!
    But if you look closely at the manufactures info you'll find that YORK for instance , gives ESP values WITHOUT filters And very intelligently then gives some instruction as to why you may for instance need 2 return elbows and filters for say a 5T unit
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  3. #23
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    Gib's Son I agree with both ideas

    Your's
    I disagree that dirty filters etc. result in higher operating costs the system is working more. It is actually working less. Take a blower and run it wild with no restrictions....amps go up. Stick board in front of the outlet and restrict flow and amps go down...it's moving less air and doing less work. Your losing efficiency, which wastes energy and is a loss of efficiency causing the system to run longer.
    I think the underlined sentence agrees with " result in higher operating costs the system is working more." that you said you disagree with

    But I like your point about amp draw. Counter intuitive isn't it!
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  4. #24
    Join Date
    Feb 2011
    Location
    New Jersey
    Posts
    649
    Post Likes
    When a furnace tune-up is being performed by reputable person/agency do they undertake such static pressure tests in supply and return and thus adjust (if possible) accordingly? Or, this is something completely out of the purview of maintenance?

  5. #25
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by genduct View Post

    I think the underlined sentence agrees with " result in higher operating costs the system is working more." that you said you disagree with

    But I like your point about amp draw. Counter intuitive isn't it!
    With a constant cfm ECM blower the amps will go up as the filter becomes restrictive.

    I assume that Gib's Son was responding to Desuperheater's statement. But here's what he actually said "Less ESP at equal CFM means the blower is working less, might last longer and will use less energy." Which is correct. HTH.

  6. #26
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes

    It should be

    Quote Originally Posted by wisepole View Post
    When a furnace tune-up is being performed by reputable person/agency do they undertake such static pressure tests in supply and return and thus adjust (if possible) accordingly? Or, this is something completely out of the purview of maintenance?
    determined at installation and bench marked. It should be checked on each maintenance call to help determine if the system is functioning propperly.

    Most companies will not check it because they do not know what it should be, or where to take the measurements.

    Reputable person/agency is a relative term.

  7. #27
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    I understand why you may think what you said was true

    Originally Posted by genduct

    I think the underlined sentence agrees with " result in higher operating costs the system is working more." that you said you disagree with

    But I like your point about amp draw. Counter intuitive isn't it!

    Quote Originally Posted by hvacrmedic View Post
    With a constant cfm ECM blower the amps will go up as the filter becomes restrictive.

    I assume that Gib's Son was responding to Desuperheater's statement. But here's what he actually said "Less ESP at equal CFM means the blower is working less, might last longer and will use less energy." Which is correct. HTH.
    BUT I believe the counter intuitive situation we mentioned should still be true even though the more efficient, and smarter moptor is going to try to hunt for the "sweet spot' delivering the CFMs it want to "shovel" into the duct system
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  8. #28
    Join Date
    Sep 2007
    Location
    Boise, ID
    Posts
    5,013
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    With a constant cfm ECM blower the amps will go up as the filter becomes restrictive.

    I assume that Gib's Son was responding to Desuperheater's statement. But here's what he actually said "Less ESP at equal CFM means the blower is working less, might last longer and will use less energy." Which is correct. HTH.
    The original discussion did not mention an ECM motor. That being said, I would have to run my own real world test to confirm ( in my mind) that amps would go up as ESP increases with an ECM motor in order to believe it. I have never tested this. On the surface it sounds logical, but before I ran real world test's on non-ecm motors, I never believed that more static = less amp draw either.
    Politicians need to be changed like diapers, and for the same reason.
    Mark Twain

  9. #29
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes

    Post

    [QUOTE=Gib's Son;11478882]The original discussion did not mention an ECM motor. That being said, I would have to run my own real world test to confirm ( in my mind) that amps would go up as ESP increases with an ECM motor in order to believe it. I have never tested this. On the surface it sounds logical, but before I ran real world test's on non-ecm motors, I never believed that more static = less amp draw eitherOTE]

    His statement was valid for PSC motors too, given that he specified "at the same cfm."

    What he meant, best I can tell, is that given the choice of a lower speed tap and and a lower ESP vs. a higher speed tap and a higher ESP, the former would consume less energy "at equal cfm."

    The fan laws will tell you the same thing.

    I brought up the constant cfm ECM blower because it's a more direct example of this effect.

  10. #30
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    I see your point

    What he meant, best I can tell, is that given the choice of a lower speed tap and and a lower ESP vs. a higher speed tap and a higher ESP, the former would consume less energy "at equal cfm."
    And you are right I misread your quote "With a constant cfm ECM blower the amps will go up as the filter becomes restrictive" and now agree that as the Smart ECM ramps up RPM trying to maintain CFMs it will use more watts to do it.

    Good call, I should read more slowly I heard you without listening
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  11. #31
    Join Date
    Oct 2011
    Posts
    8
    Post Likes
    Thread Starter
    Thank you all who responded to answer my original post. Now I have another question:
    The static pressure rating that is located on the manufacturers plate is that SP as it pertains to the unit operating in the fan or cooling mode?
    Since that heat operation is on a lower speed than cooling what pressure should I be looking for in regards to the manufacturers specs and installation design?

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •