Ventilation Rqmt in Mechanical Room
Hello pros,
Appreciate any advice you offer. We are remodeling a basement in our 10 year old home by adding a bedroom to an open space that includes a furnace and water heater on one end. The furnace is a HE gas Trane unit with intake and combustion air vented outside, that was added last year by the previous owners. The 80k BTU gas water heater has an electric blower on top, but I believe the combustion air comes from the room. This new downsized mechanical room is about 9' x 11.5' with a 9' ceiling. There was conditioned air delivered into the room before the remodel started, but that has now been sealed.
Today our contractor said he needed to add an air passage vent from one of the adjacent living spaces to the mechanical room. Do we really need to do this? Can adding a replacement conditioned air vent meet this need?
Brian
-
09-13-2011, 09:05 PM #2
No, you need the properly sized pass thru grills (ceiling and floor) to communicate to a large enough space to provide combustion air.
It's not the Brand with the fewest repairs-It's all in the install!!! Attention to detail and using the best materials!
-
09-13-2011, 09:14 PM #3
An 80,000 BTU gas fired appliance needs a free air volume of 4,000 cubic foot. So yes, you need to have combustion air added to that room.
-
09-13-2011, 10:05 PM #4
Regular Guest
- Join Date
- Oct 2007
- Location
- St Louis, MO
- Posts
- 21
I was afraid that would be the answer. We'll make it work. Thanks for the help!
Brian
-
09-13-2011, 11:41 PM #5
Kick the low efficiency pig to the curb. Install a 98% efficient sealed combustion on demand water heater and you can leave the room alone.
Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.
-
09-14-2011, 09:18 AM #6
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
Make sure they follow IFGC section 304 and IMC section 702.3,---702.3.1 and 702.3.2
also IFGC section 303Last edited by second opinion; 09-14-2011 at 09:32 AM. Reason: left out 303
-
09-14-2011, 10:46 AM #7
+1. If the hot water heater is the original builder grade unit, it's worth replacing. I'd get a HE unit as mentioned above. One AO Smith unit has enough output capacity that it can provide almost continous hot water almost like a on demand system. I plan to install one of those in the next few years to get my flue out of my chimney... or rather to stop using my 86 y/o brick probably unlined chimney as a flue.
-
10-09-2011, 02:52 AM #8
-
10-09-2011, 07:06 AM #9
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,257
-
10-09-2011, 08:02 AM #10
Professional Member*
- Join Date
- Oct 2011
- Location
- NJ
- Posts
- 120
Isn't it true that transfer air can be through openings or mechanically induced through a fan? The problem I see with the A/C vent is that there is no guarantee that the unit will be running to bring in air when the gas water heater is firing.
Couldn't a dedicated supply fan be used to blow air into the room, either a constantly running or interlocked with the water heater, as an option?
-
10-09-2011, 08:12 AM #11
You are not allowed ato put a non sealed combustion gas water heater in a bedroom, I would think you shouldn't take combustion air from that room through grilles either. Better call the code enforcement officer or fire chief on thar one first
-
10-09-2011, 08:24 AM #12
-
10-11-2011, 07:46 AM #13
Professional Member*
- Join Date
- Jun 2010
- Location
- Philadelphia PA
- Posts
- 2,139
Hello Smitty
Although there is a good reason to have and follow rules, even if they are newly instituted, I would like to point out that what boilerman said, in no uncertain terms, is what secondopinion referenced in his post.
Clearly boilerman has been very forthright and correct in warning the OP with his remarks and is right in doing so in a potentially dangerous situation.
So I think if your post could have begun with a thank you, agreed with him and then invite him to apply. The OP might have gotten the idea that boilerman's concerns were not valid.
NO GAS APPLIANCES IN SLEEPING AREAS ALLOWED
We would like to see the occupants wake up in the morningYou have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!


Reply With Quote
It`s better to be silent and thought the fool; than speak and remove all doubt. 