Results 1 to 13 of 31
Thread: Static Pressure.
10-06-2011, 01:43 AM #1
- Oct 2011
- 8
Static Pressure.
One of the measurements I make during Heat inspections is that of static pressure. The ideal static measure is: l 0.5l inches of water. So in a balanced return vs. supply it should be: l-0.25l + l+0.25l=l0.5l or simply 0.5 in wg. But this is rare if ever. Most of the time the return will be significantly higher than the supply. (-0.4/+0.1). Or since that heat is run at a lower speed the sum is significantly less than 0.5 in wg (-0.2/+0.07). Then on rare occasions I will get readings in the opposite extremes (-0.15/+0.4).
I would appreciate feed back for the following:
1.What diagnostic can be made from these example readings.
2. What potential equipment damage can result if left unaltered.
3. How would the supply and return be altered to change these readings to meet the ideal ranges.
10-06-2011, 02:57 AM #2
- Apr 2010
- southern california
- 535
I am not sure where you get that the ideal pressure is 0.5. All fans have a fan curve that compares static, cfm, and hp. The ideal static would be when the fan is operating at its most efficient point delivering the required airflow and not exceeding the rated hp.Furnaces should be checked for heat rise, blower amperes against nameplate ratings. If the recorded results are within specifications then the actual static will be inside the rating of the blower.Excessive static is usually caused by filter and evaporator coil maintenance or design problems associated with poor duct design.
10-06-2011, 05:24 AM #3
As the wizard said, .5" is not the ideal. Some air handlers are rated at .3"wg.
Fitting loss readings are sometimes required to make a decision on which alterations will make the most improvement in air flow.
10-06-2011, 07:35 AM #4
Professional Member*
- Mar 2011
- Galveston Texas
- 530
The unit itself usually has a static pressure number on it and as wizard and beenthere have said it's not always .5. Also in the units manuals and such there is an airflow data chart which shows you based on the fan being one speed and the ESP being x then your getting x amount of cfm. If that number ends up being less then what the unit is rated for then you'll need to make adjustments accordingly.
10-06-2011, 07:42 AM #5
- Oct 2011
- 8
0.5 in wc is from an inspection template given to me by my company. The comparison the temp and IFM amp to the name plate is something I also do.
So the blower wheel static rating is posted on the blower itself?
Thanks for the feedback.
10-06-2011, 07:45 AM #6
- Jun 2001
- Oklahoma City
- 2,588
Are you taking the supply reading before or after the A/C coil?
10-06-2011, 08:53 AM #7
- Aug 2007
- Northern VA 38 degrees N by 76 degrees W
- 3,251
You are on the right track
the 0.5 on the furnace name plate is the design static pressure, the 0.3 on the air handler includes the evaporator coil. Most coils have around 0.2 to 0.3 that needs to be subtracted from the furnace 0.5
Not all gas furnaces will have a coil added to the system.
A fan curve chart is supplied showing the selected fan motor, fan cfm, and at what pressure drop, or static pressure.
10-06-2011, 09:49 AM #8
Static pressure is something my trade school didn't go over as much I thought they would have. I have similar issues with SP as the OP. Anyone have any good info on SP that i can read up on? My work requires I check it on all calls, and I would like to know alot more about static pressure then I actually do...
10-06-2011, 10:17 AM #9
- Aug 2007
- 3,251
10-06-2011, 11:15 AM #10
- Jan 2007
- USA
- 13
I tried to answer this but timed out due to there being so darned many things to say about ESP, TSP and design.
.5 ESP is a middle of the road number. A decent duct design and a fairly well matched ahu/furnace running adequate CFM will typically fall into this area.
Less ESP at equal CFM means the blower is working less, might last longer and will use less energy. Saving money on duct design and construction will always spend it on electricity and fuel. Always.
Too much return pressure can be from dirty filters or filters of higher than normal efficiency. Restricted return registers or dirt and corrosion in the ductwork.
Too much supply pressure is usually a design problem. Too much flex duct. Too long a run. Too many turns.
10-06-2011, 07:36 PM #11
- Jul 2008
- Southeast michigan
- 93
All equipment has it's own tesp....don't just go by what your company says go by the rating on the furnace.... And you should take it before the coil on a furnace
10-06-2011, 07:52 PM #12
10-06-2011, 08:01 PM #13
I have also been told to check SP without involving the evap coil. Meaning for example, an upflow furnace with the blower on the bottom and the coil above, you would check SP at the bottom, and just before the evap. Is that true? Every tech I have rode with has check after the evap coil and they claim that is how you can also tell of the coil is dirty...